munchkin problem

leo g_13
leo g_13 Member Posts: 435
line, and how long is it from the reg to the boiler?

Leo G

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=286&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • MIKE6
    MIKE6 Member Posts: 102
    munchkin problem

    boiler locks out, code is f10 flame sensor or gas pressure problem.Changed 2 flame rods and gas pressure is good any ideas?I can't see the flame touching the flame rod I was thinking of pulling burner and cleaning also are those gaskets reuseable or shoulkd I have new ones on hand
  • Static versus Dynamic...

    You may have to check the gas pressure with ALL aplliances running at the same time, not just the subject appliance.

    The PRV on the meter may be having an issue, or the piping between the meter and the appliance may have an issue.

    Generally speaking, an F10 means that something ain't right.