Designing panel rads system
Wayco Wayne_2
Member Posts: 2,479
6 panel rads in a house to supplement a radiant floor in slab. I have to run the panel rad lines in slab also. I am using Buderus panel rads with TRV's and the connections are 2 inches apart. What do you use to hold the lines in place during the pour. I was thinking PVC elbows but if anyone has a better idea please share it with me. WW
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=255&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=255&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
I use those 3/4 pvc conduit bends ,they work like a charm and give a professional appearance.Just pound a piece of rebar beside them and tie strap the bend to the rebar.After the concrete has cured use a sawzall to cut the rebar flush with the concrete.0 -
Thank you
Adam for your input. WW
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Scrap pieces of PAP
is what I bend up for those. 1/2 pex easily fits inside 3/4" PAP. Make them with long arms on one end if needed. Cheap too!
If you are careful you can cut them near flush to the floor with a tubing cutter.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
how about a Steel Mate pound a piece of rebar down
lash the two pieces of 1/2" though it put two pieces of 3/4" over the top; one red one blue ....call it good0 -
Don't know the lengths or temps involved for the panels, but need you consider some sort of insulation for the panel runs (particularly supply)? Have heard that temps above 150° or so aren't recommended for slabs and if the runs are long and the temps relatively high can't you expect some significant temp drop along the way?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements