cleaver brooks watertube

Glen
Glen Member Posts: 854
can change - and make a huge diff with the air mix - I think you are on the right track.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • JSPAK
    JSPAK Member Posts: 25
    cleaver brooks watertube

    working on a cleaver brooks water tube boiler .... cant get the pilot to light....running on oil but gas pilot...seems top be excessive air going to pilot.... only one adjustment that i can see and tried several adjustments.....took off lower burner plate that includes the pilot assybley and the 3 nozzels .... havingthat off i can reach up and physically inspect the air adjustment plate ... all seems well .... well here what got me wondering ..... theres a a side access plate about 6" x 12" on the right side that gives access to lower chamber after the blower but before the pilot /burner assy.... if i wedge that open about 1 inch to relieve some of the air pressure ... pilot starts and burner runs fine ..... before i rip the whole front of boiler apart ... anybodygot any ideas
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,926
    You need Tony Conner and some of the other

    Big commercial boiler guys. They'll hook you up. I love those monsters, but am not as well-versed as I would like to be on them yet. Mad Dog

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • mark  smith
    mark smith Member Posts: 112


    if it was a fire tube, i would tell you that you had an inner door air leak ..

    i don't know what model WT you are talkin' here ...
  • mark  smith
    mark smith Member Posts: 112


    is this a model 3 ..???
  • Dan_22
    Dan_22 Member Posts: 24


    Have you checked the gas pressure to the pilot. I had a problem like this on a PVI water heater. The regulator was bad.
  • Glen
    Glen Member Posts: 854
    yes -

    sounds like too much air velocity to let the pilot light off. So then you have to ask yourself - what has changed?? The CB's I have tuned have had a VERY fine line between light off and flame failure. I found that measuring the flame signal and adjusting the pilot flame to spec numbers helps - but still needs a watchful eye to gaurantee reliability. Also check pilot gas pressures - CB's seem to like PG pressures on the low side. Other questions - FR or UV/IR? Can you witness a lightoff but not stability? Oil txfrmr ignition? Can you measure chamber pressure? Again - what has changed???
  • JSPAK
    JSPAK Member Posts: 25
    MODEL 4-2500

  • JSPAK
    JSPAK Member Posts: 25
    GAS PRESS AND VISIBLE SIGHT OF PILOT

    GOT 2 BOILER SIDE BY SIDE ..... BOTH RUNNING AT 4"..... WITH SIDE PANEL TIGHT GOT GREAT SPARK ..... AND PILOT LOOKS LIKE ITWANTSTO LIGHT ...... 2-3 LIGHT FLAMEAROUND PILOT TUBE ........ BUT WHEN I WEDGE OPEN THAT SIDE PANEL PILOT LIGHTS GAS AND ROLLS AROUND BUNER 1/2 WAY AROUND LIKE IT SHOULD BE .... 5 DV VOLT SIGNAL ... AND MAIN FLAME FIRES .. I KNOW I DEFINATELY GO EXCESSIVE AIR ..... HAD AIRDAMPER CLOSED ALL WAY DOWN TOO
  • oil-2-4-6-gas
    oil-2-4-6-gas Member Posts: 641
    .

    inspect your air damper --then check all linkage -close the air almost all the way down --then adjust --of course this is after verifying that the solenoid isn't short cycling ,after testing the ignition transformer--and cleaning ,adjusting the electrode MODEL 4's were ok i always hated the staged solenoid system like the CBH boilers --
This discussion has been closed.