pipe sizing
carl_15
carl_15 Member Posts: 21
thanks mike, you've been a great help. wher edo you live?
  • carl_15
    anthony r.
    I'm considering a 2 pipe system with baseboards. i now have 1 1/4 pipe coming out of the top of the boiler.
    1 - Does the supply pipe run THROUGH each baseboard to baseboard all around the house until it reaches the return on the boiler?
    2 - What size pipe do I run to each 3/4" baseboard? 3/4?
    3 - When I install a THV on each baseboard, do I tee-off a 1/2" bypass line above the b/b element?
    4 - Can anyone direct me to a baseboard temp regulator/ thermostat website?
  • Empire_2
    Empire_2 Member Posts: 2,340
    B&G websight is nice
    Q,1) you can pipe in series for a total of 67 ft. 3/4' base then pick up your return. It will provide you with 40,000 btu effective base. 2.) 3/4" for one loop or zone is fine if you need all that 40,000 btu. Also the boiler and the pump itself is very critical to properly design this system. Also don't forget that on that first loop of 3/4" you will see a slight temp drop as the end of the loop is reached. Sorry I didn'y understand Q # 3...
  • Empire_2
    Buffalo, NY
    Were gonna get smacked by a big snow storm today and tomarrow.......
