Is it just us?
![[Deleted User]](https://secure.gravatar.com/avatar/3877c9c466867bb6980ea26bc7a0f5ff/?default=https%3A%2F%2Fvanillicon.com%2F01d065a52c88abd78b06714048174c6a_200.png&rating=g&size=200)
[Deleted User]
Posts: 184
this AM was for not enough heat on a parallell primary/secondary job we installed this summer. The Property Manager read an e-mail he received last evening from one of the condo folks. The radiators were warm, but the apartment was cool. "Why not yesterday morning when it was 10*?" No answer.
Mr. Fixit toodled over around 10 AM. Tekmar 264 showed 138* system temp. Target was a bit higher. The culprit, as we should have known, were 2 MH Aquastats w/ the metal thumb dial. Both set @ 170*. Shut down @ 140*. That's 30*- Mr. Honeywell. Set to 200* & verified w/ the old IR, that 170* is now the actual limit. Still. I wonder why this call didn't come in when it was 15* colder outside?
Last call of the day was no heat on a steamer we installed in October. The Gartster drew this one. Alas. The boiler room operation seemed flawless. 301 GAS up & running. Water line stable as Mount Rushmore. Heat-Timer calibration dead on. Hummm. Called the Property Management folks. Apt 106 was the complainer. Knock-knock. Sure enough, the apartment was cool. Guess so. 2 of the 3 radiator valves were turned off. All 3 vents had been visited by a loaded paint brush. Some counter clockwise action & 3 #5 Gortons later - Mr. Steam was in the house. Still. I wonder why this call didn't come in when it was 20* colder outside?
Mr. Fixit toodled over around 10 AM. Tekmar 264 showed 138* system temp. Target was a bit higher. The culprit, as we should have known, were 2 MH Aquastats w/ the metal thumb dial. Both set @ 170*. Shut down @ 140*. That's 30*- Mr. Honeywell. Set to 200* & verified w/ the old IR, that 170* is now the actual limit. Still. I wonder why this call didn't come in when it was 15* colder outside?
Last call of the day was no heat on a steamer we installed in October. The Gartster drew this one. Alas. The boiler room operation seemed flawless. 301 GAS up & running. Water line stable as Mount Rushmore. Heat-Timer calibration dead on. Hummm. Called the Property Management folks. Apt 106 was the complainer. Knock-knock. Sure enough, the apartment was cool. Guess so. 2 of the 3 radiator valves were turned off. All 3 vents had been visited by a loaded paint brush. Some counter clockwise action & 3 #5 Gortons later - Mr. Steam was in the house. Still. I wonder why this call didn't come in when it was 20* colder outside?
0
This discussion has been closed.
Categories
- All Categories
- 87.1K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 58 Biomass
- 427 Carbon Monoxide Awareness
- 114 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 110 Geothermal
- 161 Indoor-Air Quality
- 3.6K Oil Heating
- 71 Pipe Deterioration
- 999 Plumbing
- 6.3K Radiant Heating
- 393 Solar
- 15.4K Strictly Steam
- 3.4K Thermostats and Controls
- 55 Water Quality
- 46 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements