Boiler over fills

I assume you used a mechanical fill device, one that activates as soon as the low water cut off drops out? IF so, you have two choices...wire in a time delay relay, or remove the feeder and install an electronic unit, like a Hydrolevel VXT feeder, that has built in time delay and quantity of feed devices. This will allow feeder to delay for a set time to allow condensate to get back in the boiler.

Comments

  • Jed Annabi
    Jed Annabi Member Posts: 1
    Boiler Overfills

    I have a stem boilers with a indirect water heater for hot water radiant heat. Just recently installed was a automatic water feeder. System works great, however when the hartford loop dumps into the boiler after the auto feeder pumps water into the boiler, it gets overfilled. what do i do with the wet return and the water feeder so that they can work with each other and not against each other causing the boiler to get flooded.
This discussion has been closed.