Trinity install done! (pics)

bill_71
Member Posts: 46
that looks pretty good for a d.i.y job. to set it up for proper operation you absolutely need to have a combustion analyzer (the old fyrite is just wayyyy to slow). keep it running on low fire by adjusting the lo fire setting on the sentry control, keep a faucet on and take your tests.adjust the air/gas as needed. the factory has told me to keep the co at around 95 ppm out the flue and you can almost set the thing up by just reading the flame sense.......
as dr. heat will attest to, i have much more experience then i ever could by going to a training course.i had to rebuild 26 of these due to factory goofs(of course nothing was admitted to) in the original design
as dr. heat will attest to, i have much more experience then i ever could by going to a training course.i had to rebuild 26 of these due to factory goofs(of course nothing was admitted to) in the original design
0
Comments
-
And asking for help
Well almost done. Just have to add the condensate loop/drain and extend the PRV down.
Here are a couple pics of the job.
Since I have had no luck finding a Pro in my area who will start this system up for either of two reasons,1. I did the install myself. 2. None have worked with a Trinity boiler before. I am considering trying it myself. Would anyone who has experiance with the Trinity be willing to give me some advice?0 -
An install to be proud of!
Very neat and tidy, easy to follow!
I like the offset backboard to make for neat wiring. Wish I had done that....
What is the triplex gas piping arrangement at the floor (3/4")? And that small electric DHW heater?
Excellent work, Andy."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
This is an addition to my house, the radiant is for the floor around our indoor pool. The gas piping your speaking of is feeding in for the mechanical room and then back out to a small heater in my shop.
The small electric water heater is for the 1/2 bath sink that services the pool area. That seemed like the best way to go.0 -
Wow!
NY Thermal should have some shots for their literature! Excellent layout and detail!0 -
Supply??
It may look nice but unless my eyes decieve me I dont see a supply from the boiler. The tapping where the relief valve is installed is where the supply pipe tapping is. It looks like the primary loop is pipe from the return port to the run of a tee, leaves the branch of the tee does a big loop and goes back to the tee.
Sorry in advance if I'm missing something
Steven0 -
Stev
Look close the supply is directly in front on the return, if you look below the circ you will see a 90 going back toward the wall then another 90 returning to the boiler. on the supply that is a 90 going up not a tee0 -
Are the rubber connections for the fresh air and exhaust from the factory? Or am I missing something here.And yes a very impressive install.0 -
Sorry, My Ipologies
Next time I will look closer before I say anything.
Nice Install, very neat0 -
nice work
Make sure you put the condensate trap on before firing; and you MUST dial it in with an analyser. Perhaps the local rep would come out and help.0 -
Two questions..
Is the secondary piping between the primary side and the manifolds big enough to handle full demand of all of the loops? I can't judge pipe size very well from the picture.
Is there a pressure regulating valve? If not, how does the system/control operate so one is not needed? OOPS, my bad, as the young hipsters say nowadays, I just noticed you have to move the prv down, I thought that might have been a purge port.
Very nice install!!!0 -
The fernco(rubber) boots are not factory. The boiler comes from the factory with solid pvc couplers but I got the fernco idea from other installs I've seen and liked that better.0 -
Primary loop is 1-1/4" and secondary loop is 1" which is large enough for the manifold.
0 -
Nice work
That is the plumbest run of pex into the manifold I ever seen!!
Obviously , a lot of planning and prep work into that, I like the 2x4 bracket for
the conduit ells also. Is that a slab sensor wire? Where does the condensate go?
The only thing now, set up with an digital analyzer.
Devan0 -
Thanks, and yes that is a slab sensor going into the last chase way. In my first post I stated I still need to run the condensate loop(which goes to a floor drain about 1 foot away) and PRV discharge pipe. Those are both done now.0 -
What are the chairs I am seeing
Tell me about the slab reinforcement. Am I seeing chairs? Is the PEX down tight to the foam insulation, with the resteel above?0 -
Yes, the pex is tight to the insulation and the rebar is on chairs above that.
2" insulation with the pex stapled to it. rebar sitting on 2" rebar chairs. Slab 5" thick.
0 -
Size of rebar? Looks like #3.
Spacing?
Really good looking job, BTW. How much DIY do you do?0 -
Gene, The rebar is #3 on two foot centers also I used 1.5lbs of fiber per yard in the concrete mix. As for my DIY experiance, I've framed many houses along with completely building 3 houses which I did the whole job except concrete, drywall and sheetmetal work(HVAC). The electrical and plumbing is no problem for me but I just don't have the analyzers or experiance to get my boiler set correctly.0 -
The only advice I can offer is you really need to have a HVAC pro who owns a combustion analyzer to check your Trinity out upon initial firing. The CO2 needs to be within careful parameters - CO also needs to be within a scale, but CO2 is the critical test for proper combustion. You did a nice looking install- compact & neat. I also like to use a neoprene connector for vent piping for easy inspecion & service. The ones I use are stainless steel reinforced band no-hub connectors.0 -
Finally found a commercial contractor who has a combustion analyzer and is going to come out this afternoon and give the install a once over, fire the boiler and make sure everything is working properly.
I've already purged all the air out, so his job shouldn't be much more than flipping the switch and testing gas pressure, flue gas and combustion.
If i'm missing anything else that should be checked, please let me know.0 -
Up and running!
Technician just left. Everything runs excellent.
Gas was 6.5" wc
CO2 was 8.3
O2 was 6.1
CO was 44
All which seem to be fine.
Thanks to all who helped.0 -
What size..
What size is the boiler and what is the heat load per
loop(s)? Just curious.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements