Freight Train Radiator
Options
Steamhead (in transit)
Member Posts: 6,688
the #6 vented too fast for the rad. The steam came up so fast that the condensate couldn't drain back, resulting in the rumbling.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Freight Train Radiator
I have a second floor bathroom radiator that vents like a freight train woke us up last night thought the vent had let go. Vent is a brand new Gorton #6, branch is the last one off the main before returning to boiler. Main is vented with a new Gorton#2. Should I try a slower venting valve? None of the other radiators in the house do this. Radiator is 3 tube, 9 secton, 20" high thin tube type.0 -
Freight Train Radiator
No takers? I switched to a Gorton#5 and it seems to have fixed the problem. I do have another question. When the boiler shuts down I have one large radiator which the air vent opens for about 15 - 30 seconds what is going on here any thoughts would help0
This discussion has been closed.
Categories
- All Categories
- 85.8K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 857 Plumbing
- 5.8K Radiant Heating
- 373 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements