BTU per foot 1.25 fin base board?
What kind of baseboard the brand? Steam or Hot water?
  • D lux_2
    D lux_2 Posts: 230
    what is the btu for 1.25 baseboard per foot
    thanks in advance
  • A.J.
    A.J. Posts: 257
    Baseboard BTU's
    will depend on the encloser and water tempeture Dlux you really need to get the manufactures lit. and figure that water temp. you are using.
    Kupetz's Plb & Htg
  • D lux_2
    D lux_2 Posts: 230
    hot water
    brand I dont know, any rule of thumb? I expect the house is over sized . I have 125 ft of BB w/ 53,000 heat loss
  • average hot water baseboard is 560btu per ft at 180deg supply that's for 3/4 inch pipe if yours is 1/2 inch then the BTU per ft is more
  • D lux_2
    D lux_2 Posts: 230
    thanks