Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Is this bad???

Is this a steam system? If so, it is caused by the system cooling down and causing a vacuum. The cause is not enough venting. More or larger main vents would take care of this. You probably don't hear the noise when the boiler is running as the vacuum is occurring at a greater rate, pulling air into the system faster than the steam pushes the air out. TK

Comments

  • Seth_4
    Seth_4 Member Posts: 7


    When my boiler stops running, some of my convectors start to hiss and sometimes whistle. I always thought that they do that when the boiler is actually running. These do it when the boiler just stops running. Please let me know.

    Thanks
  • Seth_4
    Seth_4 Member Posts: 7


    When my boiler stops running, some of my convectors start to hiss and sometimes whistle. I always thought that they do that when the boiler is actually running. These do it when the boiler just stops running. Please let me know.

    Thanks
This discussion has been closed.