church controls / low occupancy
Bill Fries
Member Posts: 5
Im working on a church that is adding a multipurpose room (gym) to get kids involved plus a nursery, a couple of classrooms, kitchen, and a nursery. They want the building air conditioned with rooftop units. I recommended to the architect installing a boiler for baseboard, cabinet unit heaters, and radiant ceiling panels (entrances). I just thought why heat the space with rooftop units and we can make the building comfortable in low-occupancy.
All radiation, ceiling panels, cab heaters, are piped with zone valves, but I am wondering what is the best way to keep costs down. DDC controls in a church that no one can use?.
I could pipe the building with 3 zones, then use set back stats.
Any suggestions for controls for a church that is HIT or MISS with occupancy?
Everything is still on the drawing board.
Thanks for the help (churches are different)
All radiation, ceiling panels, cab heaters, are piped with zone valves, but I am wondering what is the best way to keep costs down. DDC controls in a church that no one can use?.
I could pipe the building with 3 zones, then use set back stats.
Any suggestions for controls for a church that is HIT or MISS with occupancy?
Everything is still on the drawing board.
Thanks for the help (churches are different)
0
Comments
-
church radiation
Im working on a church in Michigan that is adding a multipurpose room (gym) to get kids involved plus a nursery, a couple of classrooms, kitchen, and a nursery. They want the building air conditioned with rooftop units. I recommended to the architect installing a boiler for baseboard, cabinet unit heaters, and radiant ceiling panels (entrances). I just thought why heat the space with rooftop units and make the building comfortable in low-occupancy.
All radiation is piped with zone valves, but I am wondering what is the best way to keep costs down. I hate to put DDC controls in a church that no one knows how to use.
Any suggestions for controls for a church that is HIT or MISS with occupancy?
Everything is still on paper.
0 -
church radiation
Im working on a church that is adding a multipurpose room (gym) to get kids involved plus a nursery, a couple of classrooms, kitchen, and a nursery. They want the building air conditioned with rooftop units. I recommended to the architect installing a boiler for baseboard, cabinet unit heaters, and radiant ceiling panels (entrances). I just thought why heat the space when un-occupied with rooftop units and we can make the building comfortable in low-occupancy.
All radiation, ceiling panels, cab heaters, are piped with zone valves, but I am wondering what is the best way to keep costs down. DDC controls in a church that no one can use?.
I could pipe the building with 3 zones, then use set back stats.
Any suggestions for controls for a church that is HIT or MISS with occupancy?
Everything is still on the drawing board.
Thanks for the help (churches are different)0 -
church heat
email me yr phone number. We have done seven so far and looking at more, be glad to help0 -
Ventilation
is going to be the most signifcant design constraint, not heat. In a gym/multipurpose room, the occupancy can be very dense and obviously varying greatly in activity. The IMC requires 15 cfm/person in an Auditorium environment, 20/person in a Gym (playfloor) environment. A heated makeup air unit and exhaust fans will be required, at a minimum. If the kitchen is non-residential in any way, exhaust and makeup air will also require competent HVAC engineering. You mentioned a nursury, which will also have specific ventialtion requirements. Hire a PE. Churches are different, but not that different. In most jurisdictions in which I have designed HVAC systems for churches that included classrooms and/or nursuries, the sometimes lax constraints on churches did not apply.0 -
Bill...
...have a look at tekmar tN4 Control Solutions at www.tekmarcontrols.com. OR call us at 250-545-7749. we would be more than happy to give you options available.
Regards,
Mike0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements