ft(H2O)

Jamie_6
Member Posts: 710
When calculating the proper pump size for a radiant panel do you add up all the individual head losses per loop to determine the entire systems ft(H2O)?
Thanks,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Thanks,
Jamie
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=289&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Pump head
No, the figure you want is the most restrictive loop. That, together with the total gpm for the system will determine the pump you need.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Head Loss
It's just like electricity. Circuits in parallel have equal head loss and additive flow rates. Circuits in series have equal flow and additive head loss.
If you keep the loops close in length when installing the tubing, the math is a lot easier. You can assume all the loops are approximately the same. Be sure to account for distribution piping to remote manifolds.
-Andrew0 -
Then according to the Wirsbo ADS Radiant Design Summary the total system USGPM is 5.2 @ 8.1 ft(H2O).
And according to Wirsbo ADS head loss calculator the most restrictive loop has 3.2 ft(H2O).
I'm a little confused though. When sizing my pump for the radiant panel I use the panels ft(H2O) not the systems right? Then why does Wirsbo give you the ft(H2O) calculated?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Well
There are only so many circulators from which to choose. According to the data you posted you're ok with one Grundfos 15-58. There are 3 speeds so you can slow it down if you choose.
Are you taking valves into account? Is this a single circulator system with differential pressure valve and zone valves?
-Andrew0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 105 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 949 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements