Is IBR effected by derating

Mike T., Swampeast MO
Member Posts: 6,928
With a calculated heat loss of 48,000 you won't find any condensing/modulating boiler that "cuts it close"--they'll all be quite oversized.
DHW won't be a problem unless you have a large peak demand like a big tub or a multi-outlet shower. In the case of high peak demand, use a larger storage capacity indirect...
DHW won't be a problem unless you have a large peak demand like a big tub or a multi-outlet shower. In the case of high peak demand, use a larger storage capacity indirect...
0
Comments
-
derating
Heat loss is 48,000, want to use Ultra 80 (IBR 62,000) with indirect.
Domestic load is not an issue, concerned about deration(5,000 ft) I really want to cut this close, it's my house, not a customers, am I to close?
Thanks.0 -
You'll be fine
Remember, IBR allows for pickup of the boiler and piping. The boiler pickup is damn near instant, and the piping is too if you use ODR and insulate the runs.
Radiant or Bbd ?0 -
BB
Tony, BB0 -
Existing ?
Or do you have the luxury of sizing it for low temp operation ?0 -
Well I could but,
am sinking some funds into tightening the envelope as well, BB is at design temp, so hoping modulation along with envelope will reap some benefits.0 -
Sorry--missed altitude for some reason...
From Ultra literature:
"For altitudes from sea level to 5,500 feet above sea level, the Ultra boiler requires no modifications and automatically derates itself by approximately 4% per 1,000 feet above sea level."
Even simply from I=B=R of 62,000 at sea level with 20% de-ration you still have 49,600 with a computed loss of 48,000.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements