Dynatherm Boilers
John_108
Member Posts: 21
Has anyone out there installed the Dynatherm direct vent three pass boilers. I have a customer who purchased one from the manufacture and had a friend install it. The manufacture sent the direct vent kit 4" (Feilds), a 4" barometeric damper and a 5" x 4" reducer. The homeowner ran 4" pipe off of the boiler since that is the size of the adapter and the size on the Fields kit and he installed the damper.
Problem: Customer called and said that the boiler was rumbling. Arrived and tested the system - found CO2 @ 3% CO @ 200PPM Stack Temp Gross at 400 Deg. #2 Smoke. No matter how I adjusted the system it would not work. Boiler comes with several nozzles, had a .85 found the .75 and installed it. After installing the smaller nozzle I was able to get the system running better CO2 @ 12.9% CO @ 40 PPM Stack temp @ 280 Deg. My thoughts are that the flue is to small and the flue is under a postive pressure.
Question: What they call an install book says that the flue is to be 5", But manufacture sends all 4" material. Has anybody had the same problem. I'm going back to install 5" pipe today to see if it helps.
Burner is a Carlin EZ-1 PRO Boiler is a FP-24 DV
Problem: Customer called and said that the boiler was rumbling. Arrived and tested the system - found CO2 @ 3% CO @ 200PPM Stack Temp Gross at 400 Deg. #2 Smoke. No matter how I adjusted the system it would not work. Boiler comes with several nozzles, had a .85 found the .75 and installed it. After installing the smaller nozzle I was able to get the system running better CO2 @ 12.9% CO @ 40 PPM Stack temp @ 280 Deg. My thoughts are that the flue is to small and the flue is under a postive pressure.
Question: What they call an install book says that the flue is to be 5", But manufacture sends all 4" material. Has anybody had the same problem. I'm going back to install 5" pipe today to see if it helps.
Burner is a Carlin EZ-1 PRO Boiler is a FP-24 DV
0
Comments
-
Better u than me I would walk away0 -
WALK AWAY
THEY BOUGHT IT DIRECT -HAD A FRIEND INSTALL-WHERS THE FRIEND NOW-ITS NOT RIGHT -YOU ARE GOING TO TOUCH AND THEN OWN IT FOR EVERYTHING THAT IS WRONG AND GOES WRONG--I BET THERE IS NO PERMIT ON THE INSTALL-I WOULD RETHINK THIS ONE CAREFULLY0 -
John, if you choose to proceed servicing this boiler for your new customer Please consider giving my friend Kerry Moyer a call. Hes one of the owners of Dynatherm, is dedicated to making things right and stands behind his product. Im sure he will help you out with this.
Kerry Moyer
Dynatherm Boilers
(215)536-4078
Your friend in the industry,
Alan R. Mercurio
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
Dynatherm
Thanks Alan for the number. I talked to Kerry and he has to talk to Carlins' engineers since they designed which direct vent kit and pipe sizing.
John0 -
Youre very welcome and please be sure to let us know how this all turns out. Im betting on a happy ending
Your friend in the industry,
Alan R. Mercurio
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements