System failure
Options
Ken_46
Member Posts: 2
My friend has a one pipe steam system. He did some remodeling and when the system was turned back on the 3" main line is hot 3/4 the way down then gets cold with no steam going to the risers. There are no end of main air vents and no connections to break free in the line? It is a very old system with old cast Iron radiators. Any suggestions? Thanks, Ken
0
Comments
-
Got a welder?
Drill a 1/2" hole on the top of the main about 15" from the very end. Weld a 1/2" coupling to the top of the hole and insert a Gorton # 2 main vent.
Voila!0 -
It seems that
the "'I have a problem to solve' Ken" and the "'I have the solution' Ken" have merged thanks to superior engineering and anti-schizophrenia medication.
Isn't the Wall a miracle!
:P"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
OMG
I totally missed that one. When I realized it, i almost spewed my morning drink...0 -
I assume this would be a whole lot less work then cutting the main to install an air vent?0
This discussion has been closed.
Categories
- All Categories
- 85.8K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 857 Plumbing
- 5.8K Radiant Heating
- 373 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements