Waterlogged compression tank

Andrew Siegmund
Member Posts: 3
> are you sure these tanks are just compresion <BR>
> tanks? i just replaced a pair of expansion <BR>
> tanks -they were ASME tanks with a bladder <BR>
> -these were Amtrol AX80 the older style tanks <BR>
> will have piping connected on 1 side --and a <BR>
> steel pipe plug --which covers the air valve <BR>
> ---------on the end ---- <BR>
<BR>
No diaphram, checked the drawings late last week.
> tanks? i just replaced a pair of expansion <BR>
> tanks -they were ASME tanks with a bladder <BR>
> -these were Amtrol AX80 the older style tanks <BR>
> will have piping connected on 1 side --and a <BR>
> steel pipe plug --which covers the air valve <BR>
> ---------on the end ---- <BR>
<BR>
No diaphram, checked the drawings late last week.
0
Comments
-
Waterlogged compression tank
How long would it take for a compression tank to become waterlogged if there was not an air/water separator in the system. If more details are needed let me know. Thanks0 -
Kind of like how many licks does it take.................
to the center of a toostie pop. Some systems may need draining yearly, while the house next door hasn't been maintain for years and still going strong.0 -
Auto Air Vents
Any auto air vents? They'll help speed things up.0 -
Compression tanks and automatic air vents DO NOT MIX...
And I presume that's what Uni R was trying to say, but in case it was misinterpreted, allow me to clarify. If you have the old ceiling hung expansion/compression tank, you can NOT have ANY automatic air vents ANYWHERE in the system.
Converesely, if you have a diaphragmatic type of expansion tank you MUST have automatic air eliminator/vents.
Confusing, sure. But if you follow these basic rules, and the rules of pumping away, your life WILL be much simpler.
Carry on...
ME0 -
water logged
did you drain the tank all the way down ? with knowing where you live but around here you will get any where from 5 to 15 gal of water. is the feed vale by passing? do you have a coil on the boiler for hot water? you could have a hole in the coil.
william0 -
Diaphragmatic? I like it.0 -
Sorry Mark
If it wasn't clear enough for you Mark, then yes I was saying that auto air vents will decrease the time it takes for an expansion tank to become waterlogged. It will evacuate any air that goes into solution from the tank's large internal surface area where the air and water aren't divided.0 -
some clarification
The entire system is 3200 gal. There are two plain steel (no diaphram) 75 gal tanks. It's a HVAC system with two 500 ton Carrier chillers. The system usually has only one chiller operating, but the system is cross connected so the water in the cooling coils does not heat up too much. When the system is operating the water only passes through the operating side's air water seperator. Therefore any air that is "seperated" goes into the operating side's compression tank. Therefore the other side could become waterlogged if the system ran off the same chiller for an extended period of time.0 -
are you sure these tanks are just compresion tanks? i just replaced a pair of expansion tanks -they were ASME tanks with a bladder -these were Amtrol AX80 the older style tanks will have piping connected on 1 side --and a steel pipe plug --which covers the air valve ---------on the end ----0 -
Got it..
We're on the same track, headed in the same direction :-)
ME0 -
Generally speaking...
If the two tanks were properly sized, and only one tank was "on line" then you should have ended up with a LOT of free air roaming around the system.
Normally, the tanks will be about 1/2 air and 1/2 water, and the air and water will be under pressure, the same prssure required to keep the water raised to the highest point in the system.
As far as how long it would take to water log the tank, as with any hydronic question, there is only one correct answer, "It Depends..."
I have worked on large systems like yours where they used bottled nitrogen to maintain the cushion on the expansion tanks.
Are you experiencing water logging and consequential pressure changes within the system?
Do you have one tank for the chilled water distribution system and one for the heating water distributuion systems, or is there just seperate expansion tanks at the individual heat/chill sources?
Sounds like a 4 pipe system...is it?
ME0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements