Anyone use snubbers?
Options
Vermonter
Member Posts: 57
Anyone use these between the pigtail and the pressuretrol/vaporstat and pressure gauge?
http://www.smallparts.com/products/ashcroft/accessories.cfm
http://www.smallparts.com/products/ashcroft/accessories.cfm
0
Comments
-
a tad pricey
are those prices real or list w / 40 or 50 off ?0 -
Snubbers normally used when there are pulsations in the monitored process.
This not the case regarding low pressure steam,the increase in pressure is gradul and steady. What are you hoping to accomplish? I would also think there would be an issue with fouling of the snubber.0