pressuretrol settings
Options
jim_110
Member Posts: 24
5 pounds is excessive. I would set your main at 1 1/2 and subtractive differential at 0 or .5 and see how the system responds.When a call for heat occurs out of setback ,time the first cycle and if you get multiple short cycles at the end to satisfy the stat let us know the # of cycles.
0
Comments
-
PRESSURETROL SETTINGS
Had a new Burnham V84 oil boiler installed as replacement in a single 2" main steam line house. Had problems with excessive "short cycling" and final attempt to correct was to replace the initial Pressuretrol with a Honeywell L404F unit. Service person set the Differential to 5psi and the Main to 5psi . Short cycling appears to have been reduced.
Question is whether the settings are too high; I thought that settings should be 2.5 and 0. for sgl family house.
Any risk or potential problems with higher settings? Thx for any help/advice.0 -
pressuretrol settings
I remember someone on this page saying that the Empire State building is heated by steam at 5 psi. It sounds like your tech just cranked up the pressure and did not solve the real problem. Click on "steam problems" at the top of this page. It could be a number to things --radiator venting, line venting, or plugged pigtail, etc.
.5 cut-in 1.5 cutout is the standard pressuretrol setting, anything more wastes fuel. At 15lbs psi the presuure relief valve will blow according to the tag on my boiler.
Dan0 -
The product specialist at Honeywell says L404 is a commercial control and also mentioned the Empire State Building for the 5psi.
He says that the typical home uses a PA404, usually set them in the 1-2psi range and set the differential as small as possible (1-5psi diff most models).0
This discussion has been closed.
Categories
- All Categories
- 85.8K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 860 Plumbing
- 5.8K Radiant Heating
- 375 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements