Rewire Zones to avoid Short Cycle
Joe Mattiello
Member Posts: 709
Certainly you can parallel the relay type thermostats to energize both zones simultaneously with no detriment to any of the system components. If Im correct, what youre doing is trying to increase the load to minimize the short cycling of the boiler. This may help achieve your objective, but not without some complications; if one thermostat is calling and you heat both zones the area not calling for heat may overheat. Hopefully this helps.
Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions
0
Comments
-
Rewire Taco Zone controller to avoid Short Cycle
I have two zones (Zone A Garage) and (Zone B Basement)that are relatively small and my boiler short cycles. I want to wire the Taco Zone Valve Controller so that when Zone A calls for heat Zone B also opens and When Zone B calls for Heat Zone A also opens. Could this be a problem when both zone a and zone b call for heat
Zone A has a digital thermostat with batteries and Zone B has a TekMar 510 programmable thermostat.
thank you
John
845-746-67670 -
Or you could just put in a differential bypass0 -
That won't help with short cycling.
You can interlock the zones, but then one or the other will overheat, period, probably the basement... unless somehow their loads/emitters are very, very similar.
You can do this either way, but assuming the garage calls more than the basement, I would choose that as the "lead zone".. rig it up so the basement can only get heat if the garage is calling. Or vice versa, if the basement has a real load and is finished space so temperature swings are not ok.
This may not absolutely remove all possibility of ever short cycling, but it will reduce it quite a bit.0 -
Had a similar experiance
Disconnected the wiring on the zone that was less important and left the ZV open and created one big zone... temp didn't vary that much from each other but that was inside and tripled on time0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 95 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 888 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements