Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

One Pipe Steam Baseboard.

Is there any other type of new steam rediator that i could offer them that will work on a one pipe system?????????
Room space is crittical.

Comments

  • Dawaine Stanbery
    Dawaine Stanbery Member Posts: 2
    One Pipe Steam Baseboard.

    I have a project where they have a one pipe steam system.
    They want to install "Burnham Baseray" or similar of various lengths.
    This building is a very old college dormitory, they say its not possible to change to a two pipe system.
    Any thoughts or suggestions would be appreciated.
    Thanks
  • bob young
    bob young Member Posts: 2,177
    return needed

    More than a few running feet, a return will be required or it will not work properly. it is not basicly designed for one pipe steam systems
  • bob young
    bob young Member Posts: 2,177


    burnham sunrad. cast iron rec. radiant
  • jim_110
    jim_110 Member Posts: 24


    You must remember Baseray baseboard is only 3.3 sq ft of EDR per running foot. Not much heating from them. If you know the EDR requirements per room you can look into Governale Govray Radiators. They can be recessed into a wall or stand alone only 5" deep and have plenty on iron for their size.