too much venting
William Faust
Member Posts: 168
I am thinking about using them to vent my steam risers. You said that you would not recommend using them to vent steam mains which are sort of the same thing.
0
Comments
-
too much venting
Is it possible to overvent a steam radiator and what are the effects of overventing0 -
For one...
With a cold radiator that is vented tooo fast, steam will condense very quickly, makeing massive amounts of condensate. Because of the fast venting, the volocity of steam in the riser to the radiator may impede the flow of returning condensate.
The result can be gurgling noises, or accummulation of condensate and spitting vents.
In an extreme case, where radiators are very cold, as in a church that is heated only for a service, all hell can break loose with water spitting everywhere.
You can also slow the flow of steam to other less well vented risers, mains or radiators, disrupting balance.
On some well-designed systems, depending on the flow of steam from the boiler, you'll have no ill effects with huge vents.
I vent the best I can and then solve problems that arise.
I'm sure others have lots to add to this also.
Long Beach Ed0 -
For one...
With a cold radiator that is vented tooo fast, steam will condense very quickly, makeing massive amounts of condensate. Because of the fast venting, the volocity of steam in the riser to the radiator may impede the flow of returning condensate.
The result can be gurgling noises, or accummulation of condensate and spitting vents.
In an extreme case, where radiators are very cold, as in a church that is heated only for a service, all hell can break loose with water spitting everywhere.
You can also slow the flow of steam to other less well vented risers, mains or radiators, disrupting balance.
On some well-designed systems, depending on the flow of steam from the boiler, you'll have no ill effects with huge vents.
I vent the best I can and then solve problems that arise.
I'm sure others have lots to add to this also.
Long Beach Ed0 -
Any specific valves to stay away from? I heard Varivalve by heat timer are not that great.0 -
i think gorton vents
are the best..i've had overventing issues with the varivents..never had it happen with the gortons.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
i went thru 3 varivents myself. What makes those so different from Gorton? Not worth it , theyre expensive and dont last.0 -
Varivalves
So what was the problem with the varivalves? I have them all on my rads and have nothing but good things to say about them. They make no noise and they vent fast because the rads get hot much faster in comparison to the doles and hoffmans that were on them ( they were old anyway). I wouldn't use them as main vents as Heat-Timer encourages but as vents on rads I think they're great. After a few more years I'll have to see but they're contruction seems to be far better than others on the market. Unless the poppet and seal go or the adjustable bronze collet gets fouled up then I don't see why they would cause problems. If they seem to vent too fast why not just keep the vent more in the closed position?0 -
Im curious of what the experts think of them0 -
VariValves
VariValves by Heat Timer are kind of neat, but have a major manufacturing flaw. The syphon bellows in them is mounted from the top of the valve housing, pressed into a brass machining. When they expand too much, they deform and pop out and forever seal against the seat.
Of about 500 we installed in one ill season, perhaps 120 failed the second winter and another 100 failed since then.
We opened several of them, photographed the falts and sent them to Heat Timer.
They ignored us.
We wrote several times and called -- even wrote to the president to no avail.
This could be a nice product, but it's not.
Since then we've used Gortons, with virtually never a problem.
Long Beach Ed0 -
Well that stinks considering I spent quite a bit of money on about 13 of em . . . . =(0 -
Nice explanation, thnx Ed
I have Hoffmans on all my radiators, which are fine but i plan on changing them all to Gortons by next fall.0 -
So if one fails (which none have yet) I would expect a vacuum to form or air pocket which would forever keep that rad cold?0 -
If one fails...
The radiator would not heat if it fails closed, which is how the VAriValves tend to fail.
Hey, lots of them are still working, six years later. But the failure rate was high. Simply a bug in the design.0 -
Over Venting
> Is it possible to overvent a steam radiator and
> what are the effects of overventing
Over venting a rad sometimes will allow steam to rush through the lower radiator manifold rather than the upper manifold, shutting the vent before much air can leave the rad. If you need lots of venting to bring steam to the rad, try to vent the riser more than the rad. Try to let steam into the rad no faster than it can rise up the rad columns and displace air ahead of it.0 -
True, this is called "short-circuiting" . . .0 -
Unless I'm blind...
Not one poster mentioned the impact of excessive steam pressure on vents.
NEVER run a "standard" steam system with more than 2# of boiler gage pressure. On a "vapor" system, never run over half a pound (8 oz.)
Having said that, we have used both Vari-Vent's and Gorton's and find most rads over-vented and the mains under-vented - by a bunch!
Over-venting rads creates spitting, and as already written about, surging steam and reverse flow condensate "crashing" banking and making noise that is completely avoidable.
0 -
Vari-vent
This term refers to Heat-Timer's Varivalve?0 -
Oh (;-o)
Is that what they call 'em now (;-o)0 -
Yo, Ed
Question for you. I had been considering using Heat-Timer valves to vent my supply risers, but the criticism from you and Gerry Gill unnerved me. I'm wondering what operating pressures were used that resulted in the unacceptably high (and early) failure rate. I will normally be operating at 10 oz. or less - do you think that has a bearing on whether I might suffer the same fate?0 -
Heat-Timer vari-vents
Were you using them on radiators, mains or supply risers? How quickly did they fail? Was this recently? What was your cut-out pressure?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements