Issues with Return AND Away Pumping on same boiler?
D107
Member Posts: 1,906
3 zones are on return, new HW indirect will be fourth zone pumping away. We may not use DHW priority since boiler is 4x oversized. (Putting off new boiler to when required system piping can be redone.) It occurred to me that with a heat and hot water call at same time (non DHW priority) the pushing and pulling of the opposite pumping configurations could cause some problems. (perhaps DHW prioriy would negate those problems since that would keep return pumping heating and DHW supply pumping separate.
Thanks,
David
Thanks,
David
0
Comments
-
pumping away and pushing
As long as the pumps are all moving water in the same direction, you should have no problems. Depending on the indirect and the head loss thru it, the worse that can happen is a potential loss of required flow thru the indirect. Priority control would eliminate that chance.0 -
We do it all the time.
We do not repipe anything old when adding an indirect. We just add it and pump away. It keeps the price down.
As I have seen your system, there would be no problem doing it the way we discussed (leaving the returns small, etc.)
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"There was an error rendering this rich post.
0 -
Us too
On existing boilers , we pump away from the boiler and expansion tank for the new indirect . And the heating circs are ALWAYS on the return side .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements