intermittent firing

ty_3
ty_3 Member Posts: 8
Could thermostat cause a symptom like this?
BTW, where is the low limit?

Comments

  • ty_3
    ty_3 Member Posts: 8
    burnham series 2 model B boiler

    boiler shuts off about 120 deg. regardless where the high limit is set.
    it will not stay fired to reach 180 but will cycle on and off and stay at 120

  • Weezbo
    Weezbo Member Posts: 6,232
    sounds like it is bouncing off the low limit.

  • ty_3
    ty_3 Member Posts: 8


    problem seems to be the incorrect anticipation setting on thermostat
  • Bill_49
    Bill_49 Member Posts: 25
    Anyone have an answer

    Intresting, does anyone out there have an answer.

    Bill
  • Bill_49
    Bill_49 Member Posts: 25
    Anyone out there

    Can't anyone solve this problem, I remember when this site would reply in hours.

    Bill
  • Joe Brix
    Joe Brix Member Posts: 626
    Well, Bill....

    ....I doubt that this problem is solvable without being there at the boiler with a test meter to determine why it is cycling the way you have described. Too many possible causes to diagnose in cyberspace!

    Starch
  • Bill_49
    Bill_49 Member Posts: 25
    John thanks for your reply

    My question is about the boiler, I had the same problem described above. This is not my orginal post.

    I had the same problem, no water leaking the pressure holding and the water temp never got over 120 degrees.
    I call a heating contractor and he replaced the boiler. It was a 42,000 btu with a thermocouple for ignition.

    The boiler is setting in my basement and he didn't know what the problem was, so when I see a post about this problem it must be common. Could it be the aquastat or the gas valve. The high limit switch is in the aquastat, no low water leaking the pressure is holding.

    How common is this Problem, any answers out there.

    Thanks Bill
  • ty_3
    ty_3 Member Posts: 8


    I seem to have had a incorrect anticipation setting as the problem seems to be resolved after adjusting
  • Bill_49
    Bill_49 Member Posts: 25
    Robert thanks for the reply

    I had a honneywell Programable thermostat.

    Thanks Bill
  • Steve_35
    Steve_35 Member Posts: 546
    Not enough information

    Is there voltage to B1-B2?

    Is the high limit open or closed?

    Is there still a verified call for heat?

    You need to get your DMM out and gather some information. That will quickly tell you where the problem lies.