Guess whats wrong with this brand new install???

David Sutton_6
David Sutton_6 Member Posts: 1,079
I have to give you credit for posting those pictures and willingness to ask for help !!it shows you are on the right track!!

as you can see there are alot of problems with this systemthe question is what will your boss let you do??

This boiler is not going to see to many happy seasonsAsk your boos for a free rien on repairs and use the advice thats been offered and get-r-done


David
«1

Comments

  • Mike D
    Mike D Member Posts: 9
    Guess whats wrong with this brand new install

    The company I work for put this in about 1 year ago. We have been back twice aweek ever since. Please be brutally honest.
  • Paul Pollets
    Paul Pollets Member Posts: 3,661
    Huhh?

    Just another job that was oversized and underpiped. I recommend Dan's book "Pumping Away" to start.

    If I was called in on a job like this, I'd start over. The first question should be "who sized it?" The second would be "who piped it?" There are significant piping errors on all of the "near-boiler" piping. I'm sure another Walleye will detail the problems...wish I had more time.

    I'll bet this machine is condensing. And wasting boocoo BTU's!!

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Brad White
    Brad White Member Posts: 2,399
    Let's See

    1. Pumping the return toward the expansion tank.

    2. Flow checks on the suction side of the circulators. Has to be some cavitation there. How long do the circulators last?

    3. Air vent on suction side of the Circulator Farm. (That sucks... :)

    4. Assorted leaks for whatever reasons. What does the firebox look like?

    5. Gas pipe strap supports not to code for material nor spacing.

    6. Sum of circulator flows versus pipe size of header. Seems out of whack. Was it ever summed? Too bad that second tapping was not used on the supply. Perhaps the same can be said of the return?

    I suspect venting was a common past-time?
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • Dave_4
    Dave_4 Member Posts: 1,405
    Flow checks

    Those swing checks won't stop gravity feed for one thing.
  • heatboy
    heatboy Member Posts: 1,468
    You are kidding...........

    ..........right? Are there any fitting that don't leak?

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"

    There was an error rendering this rich post.

  • ALH_4
    ALH_4 Member Posts: 1,790
    protection

    Like Paul mentioned, there is no boiler thermal protection. That vent pipe looks brand new. What is it connected to? Radiators? Baseboard? Radiant floors?
  • John Reynolds
    John Reynolds Member Posts: 22


    Wouldn't you want an airscoop or a Spirovent on the feed and get rid of the old expansion tank ?

  • don_156
    don_156 Member Posts: 87
    Sorry to say

    it looks like the whole company drop the ball.So take it easy on the installer.

    When it come times for butt kicking, it looks like everyone needs to be in line.



  • Ted_9
    Ted_9 Member Posts: 1,718
    call back

    I don't have the energy to get into what I see wrong. But i'd like to know what are the service calls that you guys are getting?

    Please list them numerically.



    Massachusetts

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    What are the call backs ...

    concerning? Twice a week? thats a lot of callbacks....I surprised they are still calling the installer...after awhile most would give up and call another company....kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • ScottMP
    ScottMP Member Posts: 5,883
    You asked to be brutal

    Your Slobs and know one cared about good piping practice.

    Scott

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • another furance

    Another boiler job done by furance company....
  • Empire_2
    Empire_2 Member Posts: 2,340
    rjbphd???

    What are you saying??? Very short sighted on your part. I love furnaces and I'll go head to head with you on boilers and design techniques any day as long as you buy the beers....:-)

    Also, Ted: Like you said, list them Numerically and you forgot to say after you run out of numbers,...List them alphabetically....lol:-)

    Mike T.
  • Mike D
    Mike D Member Posts: 9


    We have been back about twice a week to bleed air from the system. We have only had to replace one pump so far. Guys, don't rag me out I tried to tell my boss about this website. I own 5 or 6 of Dans books but my boss doesn't want to hear about these "fancy new internet ideas". Oh yeah its a 10 flat apt. building with baseboard heat.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928
    To Be Brutally Honest...

    ...it looks like some utterly clueless person destroyed a perfectly good gravity system because the homeowners wanted "zones" and perhaps headroom in the basement.

    This clueless person had obviously NEVER heard of TRVs. They also likely installed an insanely oversized boiler tried to screw big (2 1/2" or larger) pipe with 18" wrenches (maybe even a single wrench).

    "Abortion" seems to be an apt description...


  • Brad White
    Brad White Member Posts: 2,399
    In Medieval and Colonial Days,

    bleeding had as much chance of a cure.

    The air being sucked in has to be reaking havoc with the piping insides.

    Funny how these fancy new internet ideas were first written on paper by Dead Men many years ago.
    "If you do not know the answer, say, "I do not know the answer", and you will be correct!"



    -Ernie White, my Dad
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,015


    Mike D,

    If you really wan't to be in this trade and learn how to do jobs properly (and it sounds like you do because your reading Dan's stuff)

    DUMP YOUR BOSS WHO IS A SLOB AND GET A NEW JOB TOMMORROW!

    IF NOT SOONER.

    You can't learn anything from someone that stupid. Work for someone that cares and be his best employee.

    DO IT!
    ED
  • Al Corelli_2
    Al Corelli_2 Member Posts: 395

    There was an error rendering this rich post.

  • How many floors ?

    If it's 3 floors up , I'd increse the boiler pressure . And did you power purge the system ? We try to get it up around 25 psi to bleed the zones . And are you absolutely sure there is no leaks in the piping ?

    Your company is up around 100 calls for this one system ? I can see the supply pipes go out and split probably somewhere else . So pumping away would be a MAJOR job in itself . But sooner or later ( very soon I'd think ) this customer is going to give up and want a proper running system . If it was me I'd get rid of the compression tank next , throw in a bladder type , change the 30 psi relief to a 40 psi ( if the boiler is rated for higher pressure ) , crank the pressure to 25 psi. and install a good air eliminator .

    And pray for the best . Cause the next step is repiping the whole friggin thing .

    Good luck Mike .
  • Empire_2
    Empire_2 Member Posts: 2,340
    Great call EBEBRATT....

    This is a man who cares about his trade and most of all wants to correct a problem that his boss basically Say's is just fine!!!. I wish I could find people like him who can notice, ponder and want to make corrections to a job that is clearly. messed up. You are a Diamond in the rough. Don't let your boss bring you down. Look for different employment in the meantime and keep on doing what you are doing/. I am impressed!!!!!

    Mike T.
  • Mike T., Swampeast MO
    Mike T., Swampeast MO Member Posts: 6,928


    Now I see the 10-flat apartment with baseboard.

    Sure looks like the original piping and previous boiler utilized two supply tappings. Why not both on the replacement?

  • Dave Stroman
    Dave Stroman Member Posts: 766


    It is really unfortunate that all the pumps were not put on the outlet of the boiler rather than the return. At this point, without repiping everything, you can try to put a spirovent on the outlet and change the expansion tank to a bladder type. And fix the leaks!

    Dave in Denver

    There was an error rendering this rich post.

  • Mike D
    Mike D Member Posts: 9


    Ron, it's a 3 story building but we're only there during the cold winter months. We're mostly a residential company but the owner of this building is (was) a friend of my boss.
  • boomhower
    boomhower Member Posts: 1


    your boss sounds like a real piece of work. probably got company from dad hired his kids to work there cause they can do nothing else. probably kept the old man his dad hired 30 yrs ago who knows everything and nothing all in one. what a mess
  • KindyMan
    KindyMan Member Posts: 8


    Stop the maddness and first install proper backflow protection!!
  • Steven Gronski
    Steven Gronski Member Posts: 98
    Thank god his boss doesnt go to the wall

    Your lucky your boss has the mind set of a clueless one because if he ever read the wall and saw this,he would do you the favor, you would probably be fired, sued for detrament to his character, and slandsering his top notch company, if he had the money to do so, instead of wasting on having to pay the techs to keep going back to fix something. If you were in my state, id be interviewing you tomorrow for a job, just on your principles of trying to learn the right thing.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Steven Gronski
    Steven Gronski Member Posts: 98
    To bad.................

    I like the Taco circulators, you could have used the IFC and eliminated the check valves......... better yet for less electrical consumption, how about a properly sized single circulator with some nice Taco EBV zone valves instead.......To bad this badly botched job has to tarnish the Taco circulators...its like putting the pig on the lipstick......

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Marty
    Marty Member Posts: 109
    Listen to Ron

    I agree with Ron including the praying part.
  • Weezbo
    Weezbo Member Posts: 6,232
    i have only looked at one picture...

    The Leakers are eating it alive!...

    pumping at the boiler makes all the leakers even worse enemies...i did not read all your post or view all the pics. i could hazard a guess that the thing is gurgeling from time to time you are having plenty problems with the circs needing new impellers /cartridges, random off heats in random zones...How am i doing so far?

    ok i look at picture #2 and think to myself 'i would lose the fingers ...maybe the hands of someone who did that with my money.'

    picture #3 seems to say tha it has just about THE Worst location for the fill valve... having pressure problems too are we? water spilling out on the floor from time to time? what is happening is the pressure changes cause a need for water..buh Then that is too much water..so it gets rid of it..buh then it fills it back to the pressure setting.. a very Karmatic approach to adding fill water.

    What about a nice injection system? *~/:)

    call it good :)
  • RonNE
    RonNE Member Posts: 7
    Amazing

    Looks like your company will use just about whatever they happen to have in the truck, on the floor, etc. Isn't that black pipe on the water feed also coming in, pretty basic. Got your solution though, clear out the building and blow up the boiler room.
  • Mitch_4
    Mitch_4 Member Posts: 955
    MY ADVICE IS THIS!!!

    there is too much to list.

    You obviously know what is wrong, because that is what you photographed. I agree with others, use find a pro here and ask for an interview. Your bailing a sinking boat and the captain doesn't see the water in the bilge.

    Grab the lifeboat and put an extra oar in the water, and get out of that place because it will ruin futur employment if your resume says you " worked for dweeb and sons"...oh yeah that place we are always following and fixing their screw ups.

    Sorry not interested..

    get out now.

    my 2 cents

    Mitch
  • Joe Mattiello
    Joe Mattiello Member Posts: 709


    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • Joe Mattiello
    Joe Mattiello Member Posts: 709


    One of the most important fundamentals of using a conventional plain steel tank is controlling the system air, as opposed to eliminating the air with a diaphragm, or bladder type tank. A common error in an air control system is installation of automatic air vents, causing the air cushion in the tank to be depleted leaving the tank water logged and the system pressure control gone. With water logged expansion tanks the expanded water must now seek a new outlet which can be the relief valve.

    Air elimination systems encompass bladder, or diaphragm type tanks with air vents strategically placed throughout the system. However, an air separation device, with an air vent should be installed at the most advantageous location where the temperature is the highest to enhance maximum air removal. see attached document for reference
    Joe Mattiello
    N. E. Regional Manger, Commercial Products
    Taco Comfort Solutions
  • Mike D
    Mike D Member Posts: 9


    The boss told me he had peerless out about two months ago. Peerless said there is a rupture in old expansion tank and supposedly that is all he can find wrong. The new expansion tank was ordered 2 months ago. I was thinking of showing the boss this thread, maybe he'll listen to the pros because he wont listen to me.
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    that would...

    take some stones to do that...you might want to be careful and have another job lined up. I don't know this guy but it sounds to me he might not want to hear it...maybe you could put it in a way coated w/ sugar....kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • ALH_4
    ALH_4 Member Posts: 1,790
    battles

    Any battle you have with your boss will be a losing battle. In my opinion, the best path is to continue to educate yourself. Read as much as you can. Read as many of the installation manuals as you can. Keep reading The Wall. Focus on getting a job with a better employer. It's like marrying someone with plans of changing them. Not going to happen. The battles will probably never end in your current situation.

    I am sure the installation manual for that boiler has the proper piping schematics. If your boss wont listen to that, he will never listen to you.
  • shawn d
    shawn d Member Posts: 1
    oh boy

    I dont know how the installers can sleep.
    the boss/install manager should be drawn and quartered for sending mutts to the job in the first place.
    they're obviously not qualified
  • The Boiler Dr.
    The Boiler Dr. Member Posts: 163
    Cleless MUTTS

    Shaun you are soooo right! I am dealing with a similar situation. New install which has not worked properly since day 1. I will be spending the next couple months re-doing some one else's screw ups. What a mess!

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Ted_5
    Ted_5 Member Posts: 272
    WOW!

    On the bright side, I have seen worse.

    Ted
  • Steve Ebels_3
    Steve Ebels_3 Member Posts: 1,291
    It's time

    Time to break out the tinfoil hats if you're working around that very much. The ghosts of the dead men that did the original install many years ago are probably screaming at the hideous piping now attached to their once proud system.

    It needs to be re-piped.........period. Sometimes looking at a system and thinking like the water will reveal that there is no hope of it ever working correctly. This is one of those times. The boss has to bite the bullet and re-do it.