Tekmar 367

Dave_4
Dave_4 Member Posts: 1,405
Is it possible to cripple a bunch of the features on a Tekmar 367 and then use it as a simple zone controller much like a Taco SR-50x? It would take some TT leads, send a TT signal to the boiler and power some circs (I read the lit but I'm not sure if it powers the circs directly or just powers relays for circs).

Comments



  • if you use the tekmar RTUs, you can use it as a zone controller without a control head. it will power zoning devices/system pump, but you'll have to add relays for the boiler demand.