tekmar 9 stage
jrh
Member Posts: 8
i am currently bidding a job that is staging 12 triad 300,000 btu boilers for heating purposes. existng controls are triad system. bid calls for 9 stage tekmar control. ever hear of it. dont you think a six stage reset control tying in two boilers per stage would be sufficient. or are there any other controls you suggest.
thanks for any input.
joe
joe
The tekmar 268 is the 9-stage control. Here is the PDF - http://www.tekmarcontrols.com/literature/acrobat/d268.pdf
I would say it depends on what the smallest load will be. If the smallest load that will run by itself is 600,000 BTU, then a six stage control tying 2 boilers together will be sufficient. However, if there is any single load that is less than 600,000, you would be better off being able to only fire 1 boiler @ 300,000 BTU. You will have less short cycling, less temperature swings, and better efficiencies.