New Circulator for Converted Gravity Hot Water System
Steamhead (in transit)
Member Posts: 6,688
you have much more water to move than in a newer setup. So you need a bit more pump. Pauls choice of a Grundfos UP-26-65-F should be OK. Another good choice is a Taco 0010 if you don't need a 3-speed circ.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
New Circulator for Gravity Hot Water System
I have finally found a contractor here in St. Louis who will install a new circulator in a "pumping away" setup, to hopefully get more heat out of the farthest away radiators. But I want to make sure we put in the right equipment.
I have a three story house with 18 radiators that add up to about 1300 EDR. There are 3" supplies and returns in the basement with 1 1/4" pipes going in and out of the boiler, which is a 1983 Burnham P-208-WI 208,000 BTU with an IBR rating of 165,200 BTU. The pipes up to the radiators are 1". The longest 3" pipe run in the basement is about 62'.
I do not fully understand the Sizing Circulators Article, but I have been told previously in this forum that high-head, wet rotor circulators are wrong for this system.
The contractor wants to put in a PL-36 along with a generic air seperator. The PL-36 looks like it is dry, but high head. A Bell & Gossett engineering rep. said the Taco-007 I have on the return is fine and not the problem. No help there.
In the Pumping Away book, I think the Series 100 is recommended.
What is the right way to go here?
I am attaching a photo if it helps.
Thanks0 -
Circ selection
I'd be using the Grundfos 26-65 3 speed. Wet rotor is fine for this application, the #100 requires maintainence (oiling) The Grundfos pump uses less electricity and has variable speed selection.
Grundfos 15-58
See how low it will go. I can't think why it wouldn't be fine on it's lowest setting. Easy enough to change if you need medium speed.
That PL36 is way too much pump. A waste of purchase dollars and a waste of electricity.
The 007 would obviously be fine as well.
(the PL=36 uses about 240 watts vs 60-80w like the 007 or 15-58 - it will also have the water moving far too fast)
Circulator
Thanks for the ideas. I cannot find a UP-26-65-F. They have a UP-26-64-F and a UP-26-64-F/VS. The VS says it is variable speed. There is also a UPS-26-99-F.
Are these the ones you are talking about?
How would the variable speed impact the situation as opposed to the single speed?
three speed pumps allow you to play with your delta-t. fast water = smaller delta-t, slow water = greater delta-t.0
- 86K THE MAIN WALL
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 5.3K Gas Heating
- 95 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 888 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 52 Water Quality
- 41 Industry Classes