excessive amount of time for steam from peerless 61 gas boiler
jim_120
Member Posts: 1
Matt Yes that plate will provide access to cleaning between the sections with a wire brush.If you do this, shut your boiler off and remove the burner tubes from the rack below. Reason is cleaning the sections will sent crap down onto the tubes which will then also have to be cleaned. Proper Series 561 boilers should make steam at the header in approx 6-8 minutes.You can try Rhomar hydro- solv cleaner and follow directions ,it's a good product.If after that your system does not improve- then it's time for a Pro to check it.
0
Comments
-
hey! I am having trouble with steam pressure on peerless 51 gas boiler approx. 16 yrs old. presure on system went to 16lbs without shutting off. replaced the honeywell pressure swith and the pressure gage. plumber says that the system is taking too long to heat water to steam (30 min) an when pressure starts to rise is does so very slowly. no steam leaks noted in system nor steam radiators. boiler sight glass will be bouncing up and down and the gas burners are operating properly. the plumber thinks there is a lot of mud in the bottom of the boiler and if so, what is the procedure to clean out the boiler? There is a large rectangular cast iron plate on the side of the boiler depicted as a "clean out cover plate" fastened by six nuts on studs. will this allow entry into the boiler for cleaning purposes or is it for removing carbon or other residue formed by the gas burners? if not is there a product that will break up any of the mud and facilitate its removal from the boiler0 -
the boiler is a peerless series 61 gas boiler. didn't think it was clear in my original post that the plumber said the pressure problem was corrected by the new switch. the extended cycle problem is still there...0 -
You need a Steam Man
the root of your problems could be dirt, or bad combustion, or something else. Try the Find a Professional page of this site.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
what about my question regrding the flushing of any mud that may be present in the system. it is probably something i can do myself and if the problem persists, then i would seek addidion l help.
???0 -
Matt...
The reason that you're not getting answers here is because the problem cannot be diagnosed without a bit of investigating. Taking any bolts that have been in cast iron for 16 years will certainly result in some broken bolts, and you'll need a new gasket when you put it back together if you can. Se we really don't like to take stuff apart that has been together that long if we don't have to. A well-fitted boiler will have a clean-out in the return piping to permit the mud leg to be cleaned. Sometimes you can clean it through the drain valve, the relief valve etc...
Like another knowing post says, the problem could be bad combustion, low gas pressure or something more simple than gack in the boiler. Or the boiler could be steaming but the system is not letting the air escape.
If the water line is bouncing in the boiler, it oftem means that the water is dirty or has oil in it. A boiler with oil in it will take FOREVER to steam.
So as another before me has said, before you start breaking bolts, get an experienced steam man to look at the system, not just the boiler. You'll wish you did as you hear bolt #3 snap off as you try to loosten it...
Long Beach Ed0 -
I see your point. thanks for the information and the advice0 -
upon further inspection, the cast iron cover plate slides over studs mouted in the boiler. brass nuts secure the plate to the boiler. the nuts over the studs loosened with little effort and since they are on studs there is no corosion and can effortlessly removed. I did not remove them since i don't want to disturb the gasket until i am sure that the cover plate will allow access to the boiler for cleaning.
If anyone is familiar with a peerless 561 steam boiler and knows if it will allow access , please respond.0 -
Matt..
The cleanout plate allows access for cleaning the flue side of the boiler only and not the internal waterways. As there are many possible reasons for your problem, it would be best to have a good steam person take a look at your boiler and system.
BG0 -
thanks for your help0 -
thank you for your imput0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements