Water coming out of second floor radiator air valve.

finished the work..did they clen the system...all the oil from the piping will foul the water and cause the vent to spit.....wet steam

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Don_187
    Don_187 Member Posts: 5
    Water coming from air vents.

    Wet return lines in a church hall were replaced due to leaks under basement floor. About 20 feet of return line at the end of one main is about 8 feet above the floor due to doorways. The last radiator and the main air vent on this main now spit water. We capped the vent and shut off the radiator valve to eliminate the leaks. Any thoughts on this problem?
  • Don_187
    Don_187 Member Posts: 5


    The work was all done using copper pipe with solderless fittings. There are 4 other radiators on this main that are not causing a problem, it's only the valve and radiator that have a 20-30 foot run before joining the wet return.
  • Dave_4
    Dave_4 Member Posts: 1,405
    pipe diameter

    What is the diameter of the copper pipe on the 20-30 foot run?
  • bob young
    bob young Member Posts: 2,177
    return

    on a long run [ over 7 or 8 running ft. ], a return is a real plus and usually necessary for proper operation.
  • Don_187
    Don_187 Member Posts: 5


    The copper return is all one inch.
  • Don_187
    Don_187 Member Posts: 5


    A line has been added from the bottom of the radiator opposite the steam input.
  • Don_187
    Don_187 Member Posts: 5
    Water coming out of 2nd floor radiator vent.

    It appears this return was pitched incorrectly causing an airlock. Repitching eliminated the problem. Thanks to those who replied.