forced HW heating system
Dave_4
Member Posts: 1,405
How long does the water hammer sound go on for?
0
Comments
-
I have a forced HW heating system with monoflow tees. When the system is heating there is a loud water hammer through the piping. what causes this and what are the solutions. I do not believe air is the problem. Thank you.0 -
Two common things
If the pipe is copper and is clamped right to the joists you will often get a VERY loud hammer. Most often the straps are metal. Copper expands a lot and the metal clamps pinch it in place until enough expansion has taken place and it lets loose.
The other thing that sometimes happens is when you have multiple zones and fast acting zone valves are used. One ZV closes while there's a call for heat in another zone. The valve slams shut and can make a bang. That's usually a single bang.0 -
HW heating
The piping is 1 1/4 screwed the hammer starts a few minutes after the boilier starts to heat and doesn't stop until the t'stat is satisfied.0 -
Noise
Can you determine if the noise is comming from the boiler or somewhere in the piping?0 -
Spring Loaded Flow Check?
Do you have a spring loaded flow check valve?0 -
Forced Hot Water and adding hydroair unit for my basement
I have a Forced Hot Water boiler with three zones in my 1st and second floor of my home and need heat from my basement. While I have baseboard radiators upstairs that work great I do not care for them much as they get in the way. We refinished the basement as a play room and would prefer not to have baseboard heaters installed as kid typically step on them and otherwise dent them.
Can we install a hydroair wall unit? If so how much should this cost? The finished basement is about 500 sq feet.0 -
HW
There is no check valve and it seems as though the hammeris coming from the piping but it may be from the boiler.0 -
differnt thread
Seemed like this a different problem than the first thread... For the guy with hyrdo air, ur best bet is to go to Cast Iron Baseboard...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements