spirovents
Brad White
Member Posts: 2,399
for the simple reason that the pressure at the suction side is lower than on the discharge side.
(Technically the suction pressure is the same as when the pump is not running if that is where the expansion tank is connected, another issue. Point is, it is the lowest pressure in the system at that level.)
It is at this lowest pressure that the air bubbles are largest or at least consistently so, hence easier to catch. :)
In the big picture, the Spirovents are piped at the suction side because it's a handy place to connect an expansion tank, what you really want to do.
All things considered, if the low pressure big bubble theory holds, the best place would be at the top of the system on a common return line. But who would remember it was there?
(Technically the suction pressure is the same as when the pump is not running if that is where the expansion tank is connected, another issue. Point is, it is the lowest pressure in the system at that level.)
It is at this lowest pressure that the air bubbles are largest or at least consistently so, hence easier to catch. :)
In the big picture, the Spirovents are piped at the suction side because it's a handy place to connect an expansion tank, what you really want to do.
All things considered, if the low pressure big bubble theory holds, the best place would be at the top of the system on a common return line. But who would remember it was there?
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad
-Ernie White, my Dad
0
Comments
-
spirovents
Im new to heating,just read pumping away, the company I work for always uses spirovents. I was wondering if it is still as important to have circ on feed pumping away from spiro or will it work just as well on the return?0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 95 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 888 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements