from te ifo. you emailed me your radiator is about 12,000 btu (7x22 section) @ 20 sections is about 50 EDR of steam or 12k btu...from your 1st info and making a couple of preumptions...your room heatloss is around 9000 btu's...it should be big enough. the one thing that is most hard to figue out by numbers is air infiltration... my guess is that you have more than just a little. Look around and check your areas around the windows , outlets baseboards for air leakage and caulk the cracks, Is the floor insulated? Yes you could get a bigger rad but the heat will still make its way out as fast....kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
room is always cold
I have a one pipe system. The radiator in the room always heats up. The room measures 22' X 13' = 286 square feet. the room has 9.5 foot high ceiling. The cast iron radiator measures 4 feet across and 24" high with 20 fins. The thermostat reads 70 degrees, but everyone who comes into the room complains that is doesn't feel warm. There's another window in this room, but does not have a radiator below it. Can someone calculate if the existing radiator in the room is sufficient to heat this room. Or should i consider installing another radiator at the far end of the room underneath a window that doesn't have a radiator.
thank you for any replies.0 -
Where
is the thermostat located, John.
When you say it is reading 70, do you mean it is set at 70 or reads 70 in the room?
It's very possible that the thermostat is too close to the radiator and should be relocated.
Jack0 -
Or, the vent in that room may need to vent slightly faster. Does this radiator have all the sections hot before the boiler shuts off on temperature? Are the windows tight?Steve from Denver, CO0 -
what is the width...
of each section? How many tubes or fins to each section? kpc
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Walked into a room a few days ago..
this room never gets warm... i think 'hmmm... it is 82 in here maybe the guys on drugs'
or maybe it does not happen to be within his idea of warm no telling.. just thought i would share that with you...0
This discussion has been closed.
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 95 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 888 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements