ignition
Jerry Boud
Member Posts: 3
I just installed a two pipe oil feed and return. the burner
starts, runs for ten seconds the fire stops for five sec.
then resumes and finishes the heating cycle. Don't know if
the spark or the oil is the one that is causing it. I bled the pump. New transformer end of last heating season.
Bouds Stumped
starts, runs for ten seconds the fire stops for five sec.
then resumes and finishes the heating cycle. Don't know if
the spark or the oil is the one that is causing it. I bled the pump. New transformer end of last heating season.
Bouds Stumped
0
Comments
-
It sounds more like
air in the supply piping once the air passes it goes back to firing. Did you put the return in the tank so it is an inch or so above the supply? If not it can draw back air and get in the system.0 -
Thanks for the comeback Bruce,The return is 3in. above the supply line.
Boud
0 -
Then I would be looking for air
getting in at fittings, pressure or vaccum test the lines. I have had a couple of times pump strainer gaskets not tight or filter gaskets leaking0 -
Bruce Stevens Thanks
Thanks Bruce, thats what it was. The gasket between the pump filter, and the pump. Thanks again
Jerry Boud0 -
Jerry Glad it worked out
and thanks for letting me know0 -
Things to keep in mind.
Once the flame is lit, you don't need the spark any more.
With two pipe you're moving a LOT more oil. This causes higher vacuum because the more fluid you put through a pipe the more resistance there is to flow. Since one line is under vacuum the increased resistance causes higher vacuum. That can exacerbate any air leaks.
Filters need to be replaced more often because you're pumping the pump, not the nozzle.
Best bet is to install a Tiger Loop instead of a 2 pipe.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements