Gorton #2

Guest_5
Guest_5 Member Posts: 35
Not sure how long the main is. I'll have to check once I get home.

But I do know its a 2" pipe as I recently insulated it with 2" fiberglass tubings.

Comments

  • Guest_5
    Guest_5 Member Posts: 35
    Gorton #2 or #1

    Hi.

    I have a question in regards to main venting.

    Currently, my long main running to the cold side of the house has a Gorton #1 on it. It hisses after the pipe and radiators are hot.

    Should I get the Gorton #2? If so, woul dit fit? The gorton #1 is 3/4" x 1/2" (as seen here: http://www.pexsupply.com/categories.asp?cID=302&brandid= )

    But the Gorton #2 has no dimension specified by PexSupply. I want to make sure it fits into the nipple.

    Want to make sure before I order, as they cost about $50 each and don't want it to be wasted because they don't fit.

    Thanks.
  • Guest_5
    Guest_5 Member Posts: 35
    also..

    I forgot another question I have in mind:

    I can't seem to find the short main. I can easily trace and see the pipes of the long main going from the back of my house to the front and thats where my Gorton #1 is located at.

    Is it normal or fine for not having two mains?
  • Charles G.
    Charles G. Member Posts: 113
    Gorton vents

    A Gorton #2 is 1/2" MPT. You could Tee a couple of #1s together and get about the same venting as a single #2. This way you use what you have and pay a little less for what you need.
  • If there's only one main

    getting all the steam from the boiler, you need a lot of venting to get the steam to the end of the main before it starts rising to the rads. How long is the main, and what pipe size?

    "Steamhead"

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Fred Harwood_2
    Fred Harwood_2 Member Posts: 195
    #1 vs #2 Gorton Vents

    Steamhead says that a #2 is the equal of 4 #1s.
  • Guest_5
    Guest_5 Member Posts: 35
    What do I need...

    to install a Gorton #2 onto the main besides drilling? Is there an adaptor to fit into the current fitting so the #2 can be installed?