eccentric/concentric reducing couplings on hot water heating sys

is there any reason for eccentric reducing couplings being specified to be used on a closed loop hot water heating system?
i can understand if it was a steam system but its not.
any ideas?

Comments

  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Typically on pumps

    especially on the inlet (suction) side, flat-on-top eccentric reducers are used to pass air along to be vented at the volute or at least not hang up in the reducer "shoulder" before the pump suction.

    Other than that and venting enhancement in general, I have no idea where else they might be used.
  • Big Ed
    Big Ed Member Posts: 1,117
    No Other....

    .......then the installer needed a off set to keep the pipes straight or maybe it was his only reducing coulping he had left in his truck.. I know I'am always shy of them..
  • ScottMP
    ScottMP Member Posts: 5,883
    If its being

    specified than some architect has old "boiler plate" spec's and thinks he is being through.

    Maybe the building will be drained ??

    Scott

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Weezbo
    Weezbo Member Posts: 6,232
    as an off-set around metal beams

    or infront of end suction pumps like Brad says.... Steam would make far more sence ... for the most part it is an expensive way to make an offset.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,507


    I have seen this done on hot water in our area quite often. "flat on top" will get the air out easier.

    ED
  • bob young
    bob young Member Posts: 2,177
    steam fitting

    way too expensive a specialty fitting to be used when not needed. they are designed for steam work. period.