Taco i series....ratio
kevin coppinger_4
Member Posts: 2,124
my first 4 way valve this for a radiant slab and used a 1" i ser. valve by taco...I am very impressed...I have a question about weater I figured the reset ratio properly. It was about .41 on the dial...does that sound about correct for a slab >
design temp. 106 f - 72f.../ 72f- -10f = 34/82 = 0.414
outside temp today here in NH. was about 50F and the supply tep was around 85F
The slab is taking awhile to get up to temp....it was all super insulated 2' styro all about...thanks kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
design temp. 106 f - 72f.../ 72f- -10f = 34/82 = 0.414
outside temp today here in NH. was about 50F and the supply tep was around 85F
The slab is taking awhile to get up to temp....it was all super insulated 2' styro all about...thanks kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements