Pressurtrol hanging up --Repairable?
mel rowe
Member Posts: 324
Thanks for the reply. The Pressurtrol is a Honeywell PA404A (additive differential) type. It is about 18 years old.
0
Comments
-
The pressurtrol on my steam boiler is shutting off on the cut-out setting of 1.5 lbs. but does not cut in at .5 lbs. It seems to be hanging up. When I just touch the lever inside, it cuts in okay. Since this is the weekend, is there a way I can possible fix it? I see white residue around the diaphragm area inside. If this is the problem, can I boil it in vinegar water and clean it out? Thanks.0 -
What brand and model number ?
We had a bad batch of PA404s that did exactly what you describe , on new installs . The boiler would cycle once on pressure , then wouldn't come back on unless we raised the cut out and diff settings . We switched to the Honeywell mercury controlled pressuretrols and they work excellent . If you have a mercury control , make sure the level arm inside the control matches up with the hash mark . And the pigtail orientation has to be a certain way - the twist on the pigtail heats up and turns and can affect the reading .0 -
Do you check the pigtail?
> The pressurtrol on my steam boiler is shutting
> off on the cut-out setting of 1.5 lbs. but does
> not cut in at .5 lbs. It seems to be hanging up.
> When I just touch the lever inside, it cuts in
> okay. Since this is the weekend, is there a way
> I can possible fix it? I see white residue
> around the diaphragm area inside. If this is the
> problem, can I boil it in vinegar water and clean
> it out? Thanks.
0 -
Do you check the pigtail?
The pigtail could be clogged up. Remove it, blow through it. If it's clogged up you can stick a coat hanger end through it then clean it out. After you reinstall it put water in it to protect the control. It will seek it's own level. Good luck.
Rich0 -
I too...
Suspect that the "pigtail" is plugged.
AS Ron said, the orientation of the pigtail should be at a 90° angle to the boiler block.If you have a mercury control, this is WAY important. Chris0 -
I cleaned out the pigtail recently. It was pretty well clogged up. I filled with water when I replaced. This Pressurtrol doesn't have a mercury switch. I suspect it has a diaphragm that moves with the pressure and in turn moves a metal lever that actuates the on/off cycle. That's the area that looks like it has a whitish build-up around it that I wondered about cleaning by placing the lower part of the pressurtrol in a boiling water/vinegar solution.0 -
Well....
Sounds like the diaphram has failed in the pressuretrol and it's time for replacement.
Don't mess with it...either get someone to replace it or shut it down. This is a safety issue and NOT something that should be taken lightly.Make sure the pigtail is cleared upon replacement, and proprly aligned. Chris0 -
Sounds like the ideal time to switch from a pressuretrol to a vaporstat, like the one someome here gave a link for-the Honeywell L408J. In switching from the Pressuretrol PA404A (additive differential) to the vaporstat, which one would be the correct part number among the several alternatives in this link? http://customer.honeywell.com/Techlit/pdf/65-0000s/65-0287.pdf Thanks a ton for the help.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements