Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
If our community has helped you, please consider making a contribution to support this website. Thanks!
Tekmar 260/Taco zvc 404
Options
jrc2905
Member Posts: 98
I would like to use a Tekmar 260 with my existing Taco ZVC 404. Can I get the boiler demand required by the 260 from the ZVC 404.
0
Comments
-
Yes JRC
Use the X-X terminals (Isolated End Switch).
Wiring as follows:
24Vac R (+) from a Transformer to one X on 404. Other X on 404 is wired to terminal 1 on 260. Terminal 2 on 260 wires back to C (-) on same transformer.
Hope this helps. If you need further assistance, please call tekmar tech support at 250-545-7749.
Regards
Mike0
This discussion has been closed.
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 430 Carbon Monoxide Awareness
- 123 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 170 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 395 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 57 Water Quality
- 51 Industry Classes
- 51 Job Opportunities
- 18 Recall Announcements