Tekmar 260/Taco zvc 404
jrc2905
Member Posts: 98
I would like to use a Tekmar 260 with my existing Taco ZVC 404. Can I get the boiler demand required by the 260 from the ZVC 404.
0
Comments
-
Yes JRC
Use the X-X terminals (Isolated End Switch).
Wiring as follows:
24Vac R (+) from a Transformer to one X on 404. Other X on 404 is wired to terminal 1 on 260. Terminal 2 on 260 wires back to C (-) on same transformer.
Hope this helps. If you need further assistance, please call tekmar tech support at 250-545-7749.
Regards
Mike0