multistage t-stats

Gene_3
Gene_3 Member Posts: 289
common 2 transformers together, this is done often when wiring Taco ZVs #2 is common to all. This is easier when transformers have R and C designated, it is not a bad idea to fuse all your transformers.

A transformer is a new Source, seperate from your line voltage in the home and should be protected. to find this DIVIDE THE VA RATING BY THE VOLTAGE OUTPUT

THE RESULT IS THE AMPS RATING

insatll that size fuse or just a notch higher, do an amp check while it is running, funny how all commercial tarnsformers are protected and residential is not, hmmm.


You must however take your time, color code your wires, ie make white or blue common, do not mix yourself up, I am always nervous when turning on the power for the first time after wiring something like this, cuz, if you miss something, it will smoke, keep your finger on the switch when starting

Comments

  • Rich P.
    Rich P. Member Posts: 60
    Two stage two transformer tstat?

    I just installed a floor warming/hydro-air system
    and now I need a simple two stage thermostat.
    I have purchased a white-rodgers 1f85-275 but the wiring
    says to common the 2 transformers together. I am uneasy aboout this. any help?
    Rich
  • Rich P.
    Rich P. Member Posts: 60
    multistage t-stats

    Thanks for the reply:
    I have quite a bit of low voltage wiring and
    I already let the smoke out of two transformers(one was too small and the other must have backfead from the boilers transformers.
    I would love to have two seperate switches in the single tstat. Maybe like the old honeywell's with two bulbs.
    Thanks
    Rich
  • Marty
    Marty Member Posts: 109
    use a relay

    Isolate it with a relay, assuming its a heat/cool stat for the hydroair use w2 for the air and w1 for the coil of a relay for the floor. Good luck with anticipation/cycle settings floor would want something other than what the air coil will want.
  • clammy
    clammy Member Posts: 3,162
    tekmar

    how about a tekmar i believe it's a model 152-4 it has a adjustable differental and i believe a timer for the second stage also i know it's alittle bit more money but it's good stuff if not i would go with a isolation relay or two .Those relay in a box are nice adjustable coil voltage(24 v or 110 ) and a led light indicator.good luck and peace clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Gene_3
    Gene_3 Member Posts: 289
    you could also

    look at a wood/oil combo tstat, a relay would help