circulator problem

Dennis
Dennis Member Posts: 101
I have several of these installed, they have been no problem.
I used to use the B+G isolation/check valve flanges, no more though. I had two call backs for no heat due to sticking checks in these flanges.
Both where the result of floating rectoseal pipe dope in system. The contamination was not big globs believe me, it was almost invisible. The problem with these flanges is the check cannot be serviced with out disassembly and draining.

The Taco IFC can be serviced after removing the cartrige.

There was an error rendering this rich post.

Comments

  • rick_36
    rick_36 Member Posts: 19


    anybody had any problems with the circulator with built in flow check ,arrived on site and found boiler pressure 60psi and found the built in check sticking, replaced with standard pump till i can get replacement.Is one circ with check favored over another.
  • A.J.
    A.J. Member Posts: 257
    To answer your question

    No, I'm qereous why your bioler pressure was at sixty pounds though, that is up with that?
  • Ron Schroeder
    Ron Schroeder Member Posts: 998
    So far

    the only IFC I have seen stuck was when someone tried to backfeed a heating loop with 30 psi can hardly blame the check.
  • rick_36
    rick_36 Member Posts: 19


    with the internal flowcheck in circulator was closed and pump running created enough pressure. isolated circuit and changed pump ,pressure at 18.never seen that happen new pump around 200.
  • rick_36
    rick_36 Member Posts: 19


    with the internal flowcheck in circulator was closed and pump running created enough pressure. isolated circuit and changed pump ,pressure at 18.never seen that happen new pump around 200.
  • rick_36
    rick_36 Member Posts: 19


    sorry about that it was 30psi .is this common boiler system one year old
  • rick_36
    rick_36 Member Posts: 19


    sorry about that 30 psi ,is this common for one year old circulator .I like the concept.new pump 200.
  • Joe Mattiello_2
    Joe Mattiello_2 Member Posts: 94
    Was the circulator on return?



    Joe Mattiello
    Technical Support Technician
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    1160 Cranston St
    Cranston, RI 02920
    joemat@taco-hvac.com
  • Joe Mattiello_2
    Joe Mattiello_2 Member Posts: 94
    Was the circulator on return?

    Some times when purging the system with the pump on the return, and the purge valve after the circulator it is possible to fill the system with city water pressure, because the flow can not go through the pump. For your reference I have attached a recommended piping diagram for IFC pumps.

    Joe Mattiello
    Technical Support Technician
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    1160 Cranston St
    Cranston, RI 02920
    joemat@taco-hvac.com
  • rick_36
    rick_36 Member Posts: 19


    joe thanks for the post