Presssuretrol
Alan(CaliforniaRadiant)Forbes
Member Posts: 1,243
This is from the archives, for information purposes only since it seems that your setup is different:
DATE: Jan 14, 2002
SUBJECT: George
NAME: Glenn Stanton
To help clear up the confusion on your situation, the pressuretrol on the left is your operating high limit. The one on the right is a secondary safety high limit with a manual reset feature. The one on the right is there to serve as a backup for the operating high limit. The adjustments on these are different though. The manual reset limit has a front scale that is your "Cut Out" pressure. The one on the left is labeled
"Cut In". This is not the pressure that the boiler will shut off at. To determine
your cut out pressure while operating, takt the cover off that control and
look at the setting on the wheel inside. This is the differential dial. The two
settings added together is your cutout pressure (cut in & differential).
The manual reset control on the left always wants to be set several pounds
higher than the operating high limit to avoid nuisance lockouts. Be sure that
the manual reset control is set below the relief valve setting though. Hope this
helps.
Glenn Stanton
Burnham Corp.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
DATE: Jan 14, 2002
SUBJECT: George
NAME: Glenn Stanton
To help clear up the confusion on your situation, the pressuretrol on the left is your operating high limit. The one on the right is a secondary safety high limit with a manual reset feature. The one on the right is there to serve as a backup for the operating high limit. The adjustments on these are different though. The manual reset limit has a front scale that is your "Cut Out" pressure. The one on the left is labeled
"Cut In". This is not the pressure that the boiler will shut off at. To determine
your cut out pressure while operating, takt the cover off that control and
look at the setting on the wheel inside. This is the differential dial. The two
settings added together is your cutout pressure (cut in & differential).
The manual reset control on the left always wants to be set several pounds
higher than the operating high limit to avoid nuisance lockouts. Be sure that
the manual reset control is set below the relief valve setting though. Hope this
helps.
Glenn Stanton
Burnham Corp.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Pressuretrol Settings
I have 2ea Honeywell Pressuretrols on my boiler. The system runs at 5psi. I lowered the set point on 1 of them by lowering it from 5psi to 2psi and changed the adjustable differential from 2 to 1. The boiler still operates at 5psi. What is the correct setting for this arrangement? I was trying to lower it to 2psi.0 -
You may
be able to find the answer from this thread in the archives:
Reply
DATE: Apr 20, 2000
SUBJECT: pressuretrol settings
NAME: David Laverdiere
How do I set my system to run between 1/2-11/2 psi if the main scale (cut out] on my honeywell pressuretrol bottoms out at 3psi? Also the main scale must be set at least 1.5 psi greater than the diff. Right now, with the main set at 3 and the diff at 11/2 I think I,m running between 11/2 and 3. Any advice would be appreciated. D.Lav
DATE: Jan 14, 2002
SUBJECT: George
NAME: Glenn Stanton
To help clear up the confusion on your situation, the pressuretrol on the left
is your operating high limit. The one on the right is a secondary safety high
limit with a manual reset feature. The one on the right is there to serve as a
backup for the operating high limit.
The adjustments on these are different though. The manual reset limit has a
front scale that is your "Cut Out" pressure. The one on the left is labeled
"Cut In". This is not the pressure that the boiler will shut off at. To determine
your cut out pressure while operating, takt the cover off that control and
look at the setting on the wheel inside. This is the differential dial. The two
settings added together is your cutout pressure (cut in & differential).
The manual reset control on the left always wants to be set several pounds
higher than the operating high limit to avoid nuisance lockouts. Be sure that
the manual reset control is set below the relief valve setting though. Hope this
helps.
Glenn Stanton
Burnham Corp.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
the PA series controls will not effectively do what you want -these should not be used on a residential as an operating control...PERIOD for a high limit they are ok (yes they come with all new steam boilers as part of the steam trim ) you need a vaporstat to do what you want effictively,accurately and consistently0 -
even if the PA series is not accurate enough, shouldn't reducing the cut-out below 5psi lower the operating pressure. When I did that there was no change. If I install a vaporstat, would I replace both PAs or just 1? Is the 2nd PA that is set at 2psi somehow incorporated into another control like an on-delay?0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements