Monoflo

The most efficient way to bleed a monoflo system is to drive the boiler pressure up to approx 20 lbs, set the stat to call and fire the boiler up along with the circulator.
Go to each baseboard and find the vent ell/bleeder. Bleed air from each one until water comes out. Monoflo systems always take a little more patience.

Comments

  • Bryan_18
    Bryan_18 Member Posts: 3
    Monoflo

    I have 2 apartment buildings that have Monoflo systems and I need to bleed the air out of them and I’m having trouble getting the air out
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    Ah, the air bound issue....

    Bryan, I would try some of the Q&A aspects of the site as well as what I will write here.

    Start here:

    http://www.heatinghelp.com/heating_howcome3.cfm for a primer of Diverter Tee Piping, the generic name for Monoflo type systems.

    Air in any hydronic system is usually due to a number of factors:

    -Conventional air cushion expansion tank. A rich source of air to bubble up to your radiators. (Use a sealed diaphragm type of appropriate size. The air and water never see each other.)

    -Pumping toward the expansion tank (always "pump away")

    -Insufficient initial venting and purging.

    -Insufficient or non-existent air separator. (Use a Spirovent, IMHO, or one like it.)

    Sometimes in a monoflow system it is not an air problem but a flow problem. You may have circuits or radiators that are below the main (needing two tees but only having one) or having a lot of pressure drop compared to the main.

    Many variables! Several common causes.