Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Vent Rite #31
wsdave
Member Posts: 97
Steamhead,
This vent is on one of my dry returns.
Thanks
Dave
This vent is on one of my dry returns.
Thanks
Dave
0
Comments
-
Vent Rite #31
Does anyone know what the venting capacity is for a Vent Rite #31?
I cannot find this vent in the capacity chart nor anywhere on the web.
Thanks
Dave0 -
Is this
a radiator vent, or main vent?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
That's one I'm not familiar with
but it is likely too small for the job. If this is a one-pipe system, measure the length and diameter of the steam mains and dry returns and we can tell you what you need.
If this is a Vapor system, how many radiators discharge into the dry return where the vent is?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Vents
Thanks Steamhead,
No - this isn't a vapor system - just another knuckhead job.
Last year you suggested Hoffman #4 on each of my mains.
I will remove this vent once I install the main vents.
Thanks again.
Dave0 -
vent rite #31
the vent rite # 31 is and 1/8" male straight vent. vent port opening is 1/16". good for convectors, short mains and risers. maximum operating pressure is 3 psi. regards, t.p.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements