Taco 007-Z-IFC

brucewo1b
brucewo1b Member Posts: 638
I usually come up from the boiler install a Spirovent air eliminator with the extrol tank hanging off the bottom and the pressure reducing valve ie water feed teed in between the spirovent and extrol. after the extrol put in a tee to the HWM circulor then to a second tee to the heating circulator.
Check out this site and go to page 44 and you will see what I mean just make the first circulator the HWM.
http://www.buderus.net/Portals/0/Final%20Version%20G115%20(new)%20Installation%20Manual%20062204%2063030586.pdf

Comments

  • Bryan_21
    Bryan_21 Member Posts: 4
    ?

    I was wondering about installing a Taco 007-ifc for my boiler mate and if it was necessary to install a zone valve with it?

    I will have a 007 on the supply side of the boiler and then teeing off just after it to the boiler mate and I wasn't sure if I would need the zone valve to go with the circulator or should I look at the 007-Z-ifc circulator?
  • brucewo1b
    brucewo1b Member Posts: 638
    ???

    What do you mean by teeing in after it do you mean after the circulator or in the manifold after it passes the tee to the first circulator??? You sould always tee the HWM in first so that it always sees the hottest water. I have not had any problems with just using the Grundfos ifc circulators. Just make sure that you have air vents anyplace that you could trap air on that HWM.
  • Bryan_21
    Bryan_21 Member Posts: 4


    teeing off after the boiler circulator. So you shouldn't get water flowing through the boiler mate when the other zones are calling for heat?

    thanks for the help
  • Bryan_21
    Bryan_21 Member Posts: 4
    IFC

    So the IFC dosn't open unless the circulator it's in turns on?
  • brucewo1b
    brucewo1b Member Posts: 638
    Correct

    Circulator opens the ifc
  • Bryan_21
    Bryan_21 Member Posts: 4
    Thank you

    Again thank you for your help.
  • T-RACY
    T-RACY Member Posts: 10


    I am with bruce on the piping,would look at higher head pump for a boiler mate.007 to small to be ideal..
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    I agree

    I have a Super-Stor (not sure how the PD is compared to a Boiler Mate) but it uses a Taco 0010. 10 GPM at 10 feet of head. The 007 puts out 10 GPM at 7.5 feet of head by comparison.
  • Joe Mattiello_2
    Joe Mattiello_2 Member Posts: 94
    Good Choice

    Had the same set up at my own house. Works great!! the IFC does give you more flow, because no additional pressure drop through an external check valve which can add up to approx. 150 linear feet of pipe.

    Joe Mattiello
    Technical Support Technician
    Tel. 401-942-8000 X 484
    Fax. 401-942-2360
    1160 Cranston St
  • Jed_2
    Jed_2 Member Posts: 781
    Press. Drop

    through a Boilermate is approx. 3'. What's the problem? 007IFC is plenty if piping isn't 100' away.

    Jed
  • Brad White_24
    Brad White_24 Member Posts: 28
    Pressure drop

    is predicated on flow rate.

    As stated, I do not know what the PD of a boiler mate is (off the top of my head) and at what flow rate I should have added.

    I just know my vendor recommended a high-flow low-head pump for my Super-Stor and it works -quickly. I do not disagree with you on that.
  • Jed_2
    Jed_2 Member Posts: 781
    6 gpm should doit

    I'll sell a 007IFC any day over a 0010, and get the same results.
  • Brad White_24
    Brad White_24 Member Posts: 28
    You probably are right, Jed

    I never measured the DHW boiler flow. All flow goes to the heater, the faster the better. Have a few 007's and Grundfos kicking around for spares, so now they may have a home..:)

    Thanks