some problems after piping in buffer tank
Rodney Summers
Member Posts: 748
If you have continuous circ in the circuit with the headers and buffer tank and the flowchecks are swingvalves, odds are you are getting some flow in your zones. Spring loaded valves are better, say with a 1.5 lb opening pressure. The easy way ti check is to disable the continuous circ pump ad see if the zones cool off.
0
Comments
-
some problems after piping in buffer tank
We just finished piping a buffer tank to ourlow mass coipper tube boiler this past weekend. It originally had a deadended supply header with 5 individual zone pumps coming off a boiler loop and a deadended return header returning to the boiler loop.
We put a buffer tank in and piped it to the boiler via 2" copper pipe. A Taco 0010 pump pumps water into the boiler and through the heat exchanger. The water comes out of the boiler and passes through a swingcheck valve. The 2" pipe then tees to the 1.5" supply header before entering the top of the tank. At the bottom of the tank , the 1.5" return header is teed to the pipe that returns water through the boiler.
Do you have any ideas why all zones remain hot even when pumps are not running?
I will post some pics once I get the camera batteries replaced.
Thanks.
Dave
0 -
hot zones
constant circ. on buffer tank?0 -
ghost
Do the zones have check valves? If not, ghost flow (gravity)is the culprit.0 -
Here is a schematic of the system...
0 -
schematic
Here is the schematic of what we have...0 -
tank
The zones all have flowchecks just beyond the pumps. Could our expansion tank be too small? It is an Extrol model 60. But now we have about 90 gallons of water/glycol in a 50/50 mixture in the system. What would be the correct size extrol?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements