strange noises
PMyers
Member Posts: 6
No zone valves. Each zone has its own circulator, controlled by an ARGO relay panel. Noises occur more often when it is cold out, inside is normally 68 set back to 62.
0
Comments
-
circulator noise?
We have a tenant who hears a gurgle,then a whoosh, then a bang in her baseboard convectors. This is a new system, 6 zones, each with Grundfos circulator, primary secondary, with a Munchkin 199. There is no obvious pattern to this noise, maybe it happens more when it is colder.0 -
Sounds like
air entrainment followed by water hammer. I suspect it happens when the circulator starts up. A bubble of air is caught in a compromising position at an elbow, fitting or cheap hotel. (Gurgle.) It compresses (vapor lock) then releases as the forces equalize, (whoosh) followed by a slug of water heading to the next hard turn. (Bang.)
I would make sure that the circulators are pumping away from the expansion tank, and that there is an air separator, the obvious good things. I suggest that if you get the air out this goes away.0 -
Maybe too much head? Flat curve may be better. Check it out, don't just assume it's air. People get a bit away from using products designed for American systems, annamored by other stuff.
Just food for thought. jhw0 -
Could be too much head, yes
but in order for the noise and impact to occur, I would submit that there has to be a difference in density or two media together, as well.
If a consistent gurgling at a high pitch level or tone I would think velocity, too much flow. But the "gurgle, whoosh and bang" leads me to think hydraulic shock, no doubt exacerbated by, as you well pointed out, possibly too much head. A lot of circulators on one system do add up. Wonder what color they are?
Brad White (no relation)0 -
These are three speed Grundfos circulators, and the noise happens even on the lowest setting of the pump. The system has been operating for over a year, pumping away with automatic air venting. None of the other five apartments experience this noise.0 -
These are three speed Grundfos circulators, and the noise happens even on the lowest setting of the pump. The system has been operating for over a year, pumping away, with automatic air venting. None of the other five apartments experience this noise. Tenant also reports that the noises are heard randomly througout different rooms in the apartment. This is a second floor apartment in a 3 story building. We left the auto fill off for a few days to see if there was a leak causing fresh water(and air) to be introduced but pressure held steady for 5 days. Thanks all.0 -
Thermal Expansion?
That is the only "Big Bang Theory" (tm) I can come up with. Forces building up and letting go. Does not explain the gurgling and whooshing though.
What is the boiler temperature when this happens? And outdoor temperature for that matter?
Brad0 -
noise
Possibly a zone valve hammering?0 -
I thought so too, Ed
but Paul says circulators, no mention of zone valves. But you are right, the pattern of progressive noise begs the question.
Paul, might Ed be right in that you may have zone valves AND circulators? Worth checking...0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements