Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
L7224U question
carol_3
Member Posts: 397
I'll see what I can find out. Might take a day or so.
0
Comments
-
L7224U question
Hi Carol,
When the L7224U has the Low Limit disabled (cold start mode) will the aquastat still prevent the circ from turning on until the boiler is above the Low Limit? (I hope it does prevent it)
Thanks,
Ron0 -
Here we go--When the Aquastat is set to disable it works exactly like a L8148 and there is NO Low Limit so the answer is no, the circulator will turn on simultaneously with the call for heat just like a L81480
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements