Which main vent?

Steamhead (in transit)
Member Posts: 6,688
have a female 1/2" thread inside the base of the vent which is threaded 3/4" on the outside. For some reason, Gorton never included this feature on the #2.
The critical part is how much air the vent will handle. The #2 will move about 3 times more air than the #1.
A single Gorton #2 should vent your main properly.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
The critical part is how much air the vent will handle. The #2 will move about 3 times more air than the #1.
A single Gorton #2 should vent your main properly.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Which main vent?
I have a one main steam 55 feet 2 in pipe system with 2 Gorton #1 main vents.The last two risers on the main arn't heating fast enough and do whistle air. Do I need 2 # 2's and why would the # 2's which are smaller 1/2 do a better job then the bigger 3/4 # 1's0 -
Which main vent?
Steamhead
Will one # 2 be enough? I already have the fitting currently holding 2 # 1's and that hasn't been enough.Why not just put 2 # 2's in the place of the 2 # 1's already there? I would love to save the money of buying just one valve but I'm getting tired of playing around.I want it to work now whatever that may cost0 -
Pat, I had two No. 1's on each of my mains. I left one No. 1 and put a No. 2 in place of the other. Works great. Kept the old ones for spares. You should have plenty of venting with the added No. 2 on each main.0 -
Is it possible to overvent?
Is there any disadvantage to having too much venting?0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements