how to figure out water fill pressure
that explains required cold fill static pressure.
http://www.axiomind.com/downloads/coldfill.pdf
  • Dave_61
    Dave_61 Member Posts: 316
    how to figure fill pressure
    Our boiler currently runs at about 20 pis with a 50/50 glycol water mix. The lowest pressure allowable is 12 psi.
    What should we set the autofill valve at and how would I know what it is set to? Would I just watch the boiler pressure gauge to see what the pressure is when the water stops flowing?
    Thanks.
    John
  • Empire_2
    Empire_2 Member Posts: 2,340
    On a cold fill
    You are correct. 1 psi will raise water 2.34 feet roughly.
    12 psi is the factory setting and usually ok for most residential 2 story dwellings. I would consult a glycol chart though because I'll bet the glycol /water mixture has a different spacific weight that just water alone. The guy's in here are very sharp and you will get your definitive answer.
  • John_96
    John_96 Member Posts: 3
    I went to Watts
    website and found a calculation....the height in our house from the fill valve to the top of the uppermost air handler is about 37 feet (3 stories).
    So, by their calculation, it should be 37 * .43 + 3= 19 psi.
    That should also be what our expansion tank precharge is set at?
  • JimGPE_17
    JimGPE_17 Member Posts: 29
    Yep.
  • Empire_2
    Just so I know
    Did the glycol mix make a difference? Was there a chart?
  • Brad White_9
    Brad White_9 Member Posts: 2,440
    The difference in density is
    insignificant. As with water or any fluid it does vary with temperature. The attached .pdf is regarding Dowtherm. Being miscible with water, it would seem that the minor density differences would cancel each other out.
  • John_96
    I spoke with someone at Amtrol,
    and they also agreed that glycol will not change fill pressure as opposed to just water.
    EBEBRATT-Ed Member Posts: 20,128
    Expansion tank air pressure with the tank isolated from any water pressure should be set to the same pressure as the fill valve.
    ED
  • Empire_2
    Thanx Brad
    I wasen't sure that there was a diff., but I have looked @ the chart and it does make sense. I appreciate an answer when I am not sure or have other thoughts that in affect may be incorrect, but that's why "The Wall" is so great . After all if we knew everything, we would surely not be "Only Human". Again thanx.......Mike T.
  • How come...
    you have Aunty Freize in your system? IF it IS necessary, I'd not leave the make up on or Uncle Inadvertant Dillution may show his ugly face and mess up EVERYTHING...
    If you wisely chose to shut off the make up, make sure you install a low pressure/low water cut off to avoid dry firing the boiler.
    If glycolization is not necessary, get rid of it and avoid future service troubles.
    ME