panel rads

Phil_6
Member Posts: 210
I usually install panel rads on new work or new zones and I was wondering about installing them on an existing monoflo sysyem. The customer wants to replace some of their convectors with panel rads and I was just wondering if there would be any issues.
Thanks, Phil
Thanks, Phil
0
Comments
-
Shut Offs
My concern would be using the regulating or shut offs valves that some of the panals have built in , on a Mono Flow....
Cutting off a loop effects the whole zone...
I would look into using your radiators manufactors diverter valve adaptors and maybe open them up to near max...0 -
Thanks
Good point about the diverters. The Dianorm rads we use have those available, so no problem there.
0 -
I've had no
problems installing Panels using scoop or monoflow tees.
Scott
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0